I would like to daisy chain my 220V welding circuit so that I can have outlets at multiple locations. Obviously you can't just run this heavy stuff in and out of a box and make the connection with wire nuts like with 12-2 Romex. How are you guys connecting the chain?
 
To avoid these ads, REGISTER NOW!

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,433
Location
AZ
Split bolts or trade name kernies then tape up using 3m C130 rubber tape and a outter coat of 3m 33. Also there are a couple manufacturers that make multi tap blocks, Burndy is one of them.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,778
Location
Long Island
What gauge wire is it? I have wire nuts for connecting 6gauge wire. Polaris connectors are more expensive than split bolts, but the hard insulation they come with makes them fit easier in a box than a golf ball of tape.
 
To avoid these ads, REGISTER NOW!

madosta

Well-known member
Joined
Sep 4, 2012
Messages
807
Location
Michigan
Also there's lots of posts on this. Not sure if anyone has followed up with what they ended up doing or not.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,634
Location
SE MI
Old timers would cut back a section of the outer sheath and then trim about an inch of the insulation for each of the wires. The bared copper was bent into a loop and then wrapped around the appropriate screws.


EDIT : This will only work for up to 12 gauge !
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Be aware that local/state code may not allow more than one outlet on high amperage circuits. As an example in Virginia you cannot have multiple outlets on circuits greater than 20 amps.
 

RM209

Well-known member
Joined
Apr 17, 2009
Messages
892
Location
MD
Be aware that local/state code may not allow more than one outlet on high amperage circuits. As an example in Virginia you cannot have multiple outlets on circuits greater than 20 amps.

Good point; I live in suburban MD, and received the same response from my building inspector several years ago when I asked about putting two welding outlets on a single circuit.