Recently ended up at an acquaintances place and he says, keep getting shocks from metal in the house and some arcing at a panel in the garage about a hundred feet away. He was pretty much a dipstick grandson that inherit this place so I figure maybe he isn't the one that get killed so I peek. Seems the old guy did his own, looks like a bowl of spaghetti in a blender, romex hanging everywhere and he had "put in a breaker panel" some years back.
Well among other things he uses the old fuse panel in the garage, feeds 2 conductors thru an old water pipe and jumps a wire to it for the 3rd using it as a neutral. Dipstick was trying to force rubber in the joint at the sub, he hard piped all the way, loose connector causing the arc. ha
For convenience the old guy had ran a 12/2 between to feed a light from the house.
Well, this house needs it all and dipstick isn't a guy I wanna work for, broke **** type too boot and I knoww,,,,,,, but I disable the light circuit, twist the 12's together and connect from neutral bar to N bar, The house looked fairly nice but the wiring should have been condemned and I admit here to doing that but wont elsewhere,,, ok,,, I didn't really wire it that way but should have,,, ha This place been giving shocks for years, I might have tossed a 30A fuse in the trash while I was at it. What a deal.
Funny thing was,,,, "didn't hardly make any spar at the panel when we using the arc welder" hahaha,,, which they wonder why wasn't working,,,, maybe about 50A too low was the reason. Some people shouldn't be allowed near tools or have them on their persons.
Well among other things he uses the old fuse panel in the garage, feeds 2 conductors thru an old water pipe and jumps a wire to it for the 3rd using it as a neutral. Dipstick was trying to force rubber in the joint at the sub, he hard piped all the way, loose connector causing the arc. ha
For convenience the old guy had ran a 12/2 between to feed a light from the house.
Well, this house needs it all and dipstick isn't a guy I wanna work for, broke **** type too boot and I knoww,,,,,,, but I disable the light circuit, twist the 12's together and connect from neutral bar to N bar, The house looked fairly nice but the wiring should have been condemned and I admit here to doing that but wont elsewhere,,, ok,,, I didn't really wire it that way but should have,,, ha This place been giving shocks for years, I might have tossed a 30A fuse in the trash while I was at it. What a deal.
Funny thing was,,,, "didn't hardly make any spar at the panel when we using the arc welder" hahaha,,, which they wonder why wasn't working,,,, maybe about 50A too low was the reason. Some people shouldn't be allowed near tools or have them on their persons.
Last edited: