Dayton electric heater issues.

budman80

New member
Joined
Feb 15, 2015
Messages
4
Hello guys, I'm new to the forum. And could use a bit of advice. I've recently been work on a small hobby room / pub in my garage. My brother in law gave me a old Dayton 2E669B electric heater, never been used. After talking to a friend that does HVAC he told me I should be able to just use a switch instead of a thermostat so I used a 120v light switch. The heater worked as it should except one wire that comes from one of the 120 legs gets hot. Hotter than I feel comfortable with. I've been scratching my head for days. So my question is would a line volt thermostat do anything different than the switch? It did come with a wiring diagram so I'm pretty sure everything is where it should be. Thanks for taking the time to read this.
 
To avoid these ads, REGISTER NOW!

ambenz

Well-known member
Joined
Dec 12, 2010
Messages
4,236
Location
NW Chicago Suburbs
Could you show us, in a wiring diagram, how you have the whole unit wired?
Sounds like the wire you talking about in drawing amperage.
What is the gauge of the wire in question?
 

crab

Well-known member
Joined
Jan 8, 2015
Messages
940
I have a service box in my garage and I wired the heater into it. That wire is getting hot because it isn't big enough. My heater has a built in thermostat, it's a Dayton I got from grainger, actually it's on right now. It isn't very big but once I get it warm I'll turn it down or it'll get hot out there. My garage is insulated and dry walled but the garage door isn't.
 

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
Whats the voltage and amperage of the unit? and how do you have it hooked up?
 
OP
B

budman80

New member
Joined
Feb 15, 2015
Messages
4
KIMG0062.jpg

KIMG0060.jpg
The switch is just temporary to make sure everything works. The wire in question is the one I have the probe on.
 

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
I am surpised that it does not have a contactor in the circuit? Do you have an amp probe (anything to measure the current) if so, put it on the wire in question and see what its drawing, looks to me that its going to the element.
 

ambenz

Well-known member
Joined
Dec 12, 2010
Messages
4,236
Location
NW Chicago Suburbs
From what I can see...that's almost 24.5 amps going through the wire and switch!!!!:shocking:
Stop...now!
Might get a larger gauge wire...10 awg at least!
Those switches are usually only rated for 20 amps.
The specific thermostat for that heater had a duel throw relay in it rated for at least 30 amps with 2 separate contacts.
I bet the switch is getting warm too!
The wire is very warm for that reason!
Best to get the "special" thermostat rated for that unit...it was made to handle the amprage.
 
Last edited:

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
From what I can see...that's almost 24.5 amps going through the wire and switch!!!!:shocking:...

Wrong!

That heater is rated at 208 volts, not 240 volts. At 240 volts the current goes up to almost 29 amps, power from 5 KW to about 6.9 KW. I'm not sure, since it has no 240 volt rating on that plate, whether it can be safely be used on 240 volts. :scared:
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
PLEASE TURN IT OFF NOW AND CALL AN ELECTRICIAN!!

No dispect intended, but that model is a 208/240 VAC unit. You can't safely substitute a 120 VAC 15A light switch for the proper line voltage controls.

Tommy
 
Last edited:

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
Well, it can be wired with a 1 or 2 pole T-Stat, its wired for a 1 pole and he has a 15 amp switch in place of the T-Stat, if the 15 amp switch is to small, then the wiring is also. Have you had this heater or just picked it up? just curious what size breaker do you have this on? just wondering if all original parts are/were there or if someone else has worked on this? maybe?
Cant really see the element wiring that well?
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
B

budman80

New member
Joined
Feb 15, 2015
Messages
4
I used a 40 amp breaker and 8/3 wire.
The heater has never been touched to my knowledge. I had to break out the metal holes on the back to connect it, and the wire diagram was tucked in the wire compartment in great shape.
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
PLEASE TURN IT OFF NOW AND CALL AN ELECTRICIAN!!

No dispect intended, but that model is a 208/240 VAC unit. You can't safely substitute a 120 VAC 15A light switch for the proper line voltage controls.

Tommy

No, it is a 208 volt only unit. Again, it is not safe to operate at 240 volts. Of course the internal wiring is heating up--it's overloaded.
 

dave67fd

Well-known member
Joined
Apr 25, 2011
Messages
872
Location
Southern NH
No, it is a 208 volt only unit. Again, it is not safe to operate at 240 volts. Of course the internal wiring is heating up--it's overloaded.

Although the nameplate is listed for 208 (Typical commercial single phase from a 3 phase system) the schematic lists 208/240/277 single phase supply.

It is a heater and will run fine on 240 volts. The listed current will be lower at 240 than at 208.

OP, Remove the light switch and install with a rated LINE voltage thermostat with the properly sized wire. Better yet have an electrician wire it for you before you burn your place down.
 

Syberia

Well-known member
Joined
Jan 13, 2014
Messages
1,451
Location
Perris, CA
The heating element has a set resistance, unless there are multiple elements and multiple wiring configurations for the unit. If you increase the voltage over a set amount of resistance, the current also increases proportionally in a resistive load. 240 volts will pull more amps and output more watts of heat than 208.
 

JCByrd24

Well-known member
Joined
Jul 21, 2005
Messages
493
Location
Bath, ME
Another vote for more amps and higher voltage, 28-29 amps is what I calc as well and about 6600W.

V=IR so I=V/R. Raise voltage and keep resistance the same means more amps and more watts because P=I^2 x R. Google any resistive heater rated for 208/240/277, all increase wattage with voltage. You are running near double the rated switch capacity so there is your problem. Most line voltage thermostats are rated for around 22-23 amps so you need a heavy duty one rated for 30A.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
The wiring diagram is generic for that model heater. Since the data plate specifies only 208 volts, especially since the motor is only 208 volt, it won't work properly on 240v. Fan will run slow, and possibly overheat eventually.

Charles
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
Wiring will have less amp load at higher voltage.

If it's a 208 volt only why does the wiring diagram say 208, 240 and 277.

The resistance of the heating element is the same, so 240v applied will lower the current flow. 277 will lower the amp draw more but the heater will still be a 5.0 kW heater.

High voltage is NOT going increase the KW output of the heater.

Back to basics. Volts X amps = watts

The switch needs to double pole or single pole with a jumper according to the wiring diagram .............done with the correct amp rated switch and wire.

Not sure where you got your degree in electrical engineering, but you got cheated. Learn the basic electrical rule: Ohm's Law. Now tell me how your statements above meet Ohm's law?

Although the nameplate is listed for 208 (Typical commercial single phase from a 3 phase system) the schematic lists 208/240/277 single phase supply.

It is a heater and will run fine on 240 volts. The listed current will be lower at 240 than at 208.

OP, Remove the light switch and install with a rated LINE voltage thermostat with the properly sized wire. Better yet have an electrician wire it for you before you burn your place down.

The name plate describes the unit, not the schematic. The schematic is generic.

I'm outta here, there is so much bad information here that it is a waste of time. It is the wrong heater for the application, and I've said all I need to say.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
No, it is a 208 volt only unit. Again, it is not safe to operate at 240 volts. Of course the internal wiring is heating up--it's overloaded.


I totally agree that the unit is only rated for 208. Since no nameplate or diagram was posted at the point I replied, I only went by the WW Grainger model number listed by the OP. Their website called it 208/240...:dunno:

Tommy
 
Last edited:

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Good thing you left because, you are dead wrong or just do not understand the concepts here: ( which is very scary)

https://www.google.com/#q=volts+times+amps+equals+watts

Suggest you read about the first tens searches on simple V x A = W
Or maybe run out the garage and look at multi voltage motor name plate that wil show the amps cut in half when switched from 120 to 240v. The power of the motor is the same. The concept and applied formula is the same.

Actually, you are the one who is wrong. If resistance stays the same and voltage increases, current increases. The motor current drops at the higher voltage because there are two different windings for the two voltages...

Tommy
 
Last edited:

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
I agree on the winding change......and the heater is most likely a single voltage unit ?
And possible the schematic is generic for several different heating elements used in the same heater box.
 
Last edited:

kogerat

Member
Joined
Feb 8, 2015
Messages
13
Location
Spokane WA
The whole thing looks pretty scary, but the OP could probably get away with it if he used a switch rated for 250VAC @ 30 AMPS and #10 wire, that is if he didn't electrocute himself first!
 
Last edited: