dead light/recp...please help!!!

that-guy

Well-known member
Joined
Sep 6, 2012
Messages
603
Location
NoVA
ever since I moved into my house almost 2 years ago, a light post out front has not been working. it has a light sensor on it, so it should only come when dark. to activate it, there is a light switch by the front door

there is also a GFI receptacle on the house in line with the light post that is also inactive, which the power and ground for the light post is tied into...IE, both the light post and GFI are run off of the same switch inside of the house

I have replaced the sensor on the light post, the GFI with a brand new one, and have swapped the light switch in the house with known good ones and that switch has worked in other places of the house. only thought at this point is that there is a break in the wiring somewhere, I just have no idea how to do that

the wiring is about 20" underground and is in PVC tubing. my biggest question to you all is, how would I go about testing the wiring to find where is the problem is? I know a few functions of a multimeter, but not how to do this
 
To avoid these ads, REGISTER NOW!

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,966
Location
Niagara Region, Ontario, Canada
set the meter to AC volts , check the line side of the switch to see if you have power, if yes ,check the load side. remove the GFI and probe the line side ( coming from the switch, if there's voltage there . you say the gfi doesn't work so likely no power there, or it's hooked up wrong. finally do the same for your pole
 
Last edited:

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Yeah you need a testor to check for power or it will be real difficult. The switch you are turning may not even be the right one. Test the switch first and then the gfi, if power at switch and none at gfi then it may be a splice box in the basement or in the switch box.
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
how would I know the difference between line side and load side?

Line side is power coming in and load side is going to the post. If you have a wire coming from back of box from inside that's likely the line unless both sets of wires come through there. You could always remove gfi, wire nut wires and turn switch on just to see if you have power.
 
OP
T

that-guy

Well-known member
Joined
Sep 6, 2012
Messages
603
Location
NoVA
Got home today and checked for voltage...as I suspected, everything at the switch is fine. The GFI nor post have power

Sent from my DROID4 using Tapatalk
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,268
Location
Penngrove, California
Did you check both the line and load side of the GFI, (I am assuming it is a pass thru type)?

Are you sure the switch you are operating is the one for the porch light?
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,071
Location
Modesto, CA
Most GFCIs are labeled line side and load side on the back. But if u have no power on either black wire coming into the GFCI box, then the problem i between the switch and GFCI. One way to test the hot(black) lines is to plug an extension cord into a known good outlet. Then test between the neutral on the cord and the hots in the j box.
 
Last edited:
OP
T

that-guy

Well-known member
Joined
Sep 6, 2012
Messages
603
Location
NoVA
from the way my house is layed out, it looks like the wires would be following the outside wall of the house, which goes around my son's play room to get from the switch to the GFI, and there are several reptacles in there, so i will cut power to the switch panel and see if anything in the play room gets cut as well, so make sure this thing isn't tieing into anything else...

this damn house has been nothing but trouble because of really lazy electrical work
 
OP
T

that-guy

Well-known member
Joined
Sep 6, 2012
Messages
603
Location
NoVA
yes, and basement...the GFi is located behind a bush and is directly in line with the light post. i can see about 18" of the PVC coming straight up out of the ground and going into the receptacle box
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
Sounds to me that you have an open circuit in one of the recp's in the play room. Turn off the power and pull everyone out. Turn the power on and turn the switch on. Check each rec'p with a tester. I recommend a no touch tester to do this quickly and safely. When you find it, turn the power off and rewire all of your recp's so that the power does not go through the lugs. Only the GFCI should be wired that way. This is called pig tailing and joins the whites, blacks and grounds with nut and a supply to each screw on the recp. Use stranded wire for the pig tails as it folds up better in the box.

You will now have a continuous (switched) power lead to the GFCI and lamp. It doesn't pass through the side of each recp in the circuit.
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
So,the issue is from switch to gfi, I would see if you can see a wire that comes into the basement from outside. You may find out that switch your turning doesn't do the post light or gfi. Your last option is to just run a wire from switch down to basement and over to gfi.
 