I am in no way tied to the dedicated service and appreciate the insight. It sounds like a 100 amp sub panel will likely be the way to go- any ideas on cost of running 250' wire to support this amperage?
There are, and I am guessing here, perhaps 50 individual threads on 'how big a wire do I need for my 2xx ft line to my shop with a 100A service and how much will it cost.'
These threads have all the details, calculations, pros and cons of using conduit versus direct bury..>AL vs CU... 90 vs 100A etc etc
So you distance- from the house panel out of the wall, into the ground, across the ground, then up into the garage through the wall and into the panel is 250? Not 240? Not 260? It can matter.
You can run #1/0 Copper in conduit 277 feet at 100A
You can run #3/0 Alum in conduit 266 feet.
3" Conduit is 1.50 a foot. Im going to roughly estimate that thhn is 1.60 a foot time 3 plus $1 a ft for the ground. So 1.50+4.80+1=7.30 a foot.
Approx 2k in materials