Derating question....

Silent One

Active member
Joined
Aug 31, 2011
Messages
32
I have a 60 amp sub panel from my main 200 amp panel in an unfinished basement. These were installed by the electrician when the house was built in 2001. The sub panel has a 34" long 2 1/2" protective sleeve up to the cavity between floor joists into which all the branch circuits enter and pass to the sub panel. There are 10 current carrying conductors (including neutrals - a total of 5 runs consisting of 12-2 and 12-3 nm-b) and there appears to have been no consideration for derating of the conductors. Should there have been? Will this affect running additional circuits through the same sleeve as the sub panel is only 1/2 full (provided the feed to the subpanel is not overloaded)?
 
Last edited:
To avoid these ads, REGISTER NOW!

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,038
Location
Minneapolis
Assuming you're in the US so your wiring needs to meet NEC requirements, there is a provision for installing multiple NM-B cables through a short conduit sleeve without derating issues, but I'm not sure of the maximum length for the sleeve - I was thinking it was 24", but a quick look around online indicates it may be longer.

Hopefully one of the other guys with more experience in residential work can provide a more definite answer.
 
OP
S

Silent One

Active member
Joined
Aug 31, 2011
Messages
32
Thanks - yes, I am in the US. I also saw the 24" length restriction in the NEC but then also ran across arguments that derating did not apply to my particular instance as mine would be considered a sleeve and not a raceway.
 
To avoid these ads, REGISTER NOW!

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,675
Location
Maine
Thanks - yes, I am in the US. I also saw the 24" length restriction in the NEC but then also ran across arguments that derating did not apply to my particular instance as mine would be considered a sleeve and not a raceway.
Not sure it matters if its a sleeve( i doubt their is a definition of a sleeve in the NEC) or a raceway. If its over 24 inches it must be derated according to NEC and I think thats true even if you wire tied the NM-b together with wire ties aka bundling.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I am all for code compliance but here is a place to use some sense with the intent. The N in 12/3 may not count as you may know but are these hot highly loaded circuits? You have already derated them likely, these are not all fully loaded above 20A and while the distance of this sleeve may be stretching it the concern from heating here is really moot. That's a big pipe and its short, no worry. You can only pull so much from a 60 anyway.
 