Ordered a welder that is rated at 25.5amp when running it at 200amp, so I have an idea of what to run to my welder outlets in the shop build.
1. A minimum of 30amp breaker looks like it should be enough. Is there any reason to up size to a 40amp?
2. I have 10awg THHN wire being used for almost everything except grounds. 10awg Cu is rated for 40amps. Shop will not be air conditioned, Texas heat, and the wire will be in 1" EMT. Looking at NEC 310.16, I think I should be derating the THHN based on ambient temperatures. If I use 110F (43C), I would have to deregulate by 0.87 bringing the 10awg down to 34.8amps. This will be the ONLY circuit in the EMT, so it has 3 CCCs.
If I need to use a 40amp breaker, I would need to run bigger wire (8awg), right? So back to question 1, should I use the bigger breaker and get bigger wire now before I run the circuits in the shop?
Thanks.
1. A minimum of 30amp breaker looks like it should be enough. Is there any reason to up size to a 40amp?
2. I have 10awg THHN wire being used for almost everything except grounds. 10awg Cu is rated for 40amps. Shop will not be air conditioned, Texas heat, and the wire will be in 1" EMT. Looking at NEC 310.16, I think I should be derating the THHN based on ambient temperatures. If I use 110F (43C), I would have to deregulate by 0.87 bringing the 10awg down to 34.8amps. This will be the ONLY circuit in the EMT, so it has 3 CCCs.