Construction just completed on my new 24 x 30 building, and I'm starting to think about the electrical. Due to budget constraints the electrical couldn't be completed at the same time, and will have to be added a few months down the road.
I've been doing A LOT of reading, on this forum and other sites, and I think I have a good start, but I'd like to get some input on my plans. I'm not un-familiar with electrical codes (permit drawings as part of my job), but the maximum extent of my electrical install knowledge is adding a circuit and wiring for my compressor in the main house garage.
The shop is in Florida, so 2017 NEC still applies. As I said, 24 x 30, 9' eave height metal building (Carolina Carports type), just a one man hobby shop. No electrical on the permit since it was originally going to be a while before I could afford it, but I will be pulling a permit when I do the work. One thing I screwed up on and DIDN'T do was add an UFER prior to the slab being poured. I planned to, spoke to the construction super about it, then the concrete day came & we all forgot about it until it was too late. So here is what I'm planning so far:
Loads:
The run is about 180 feet including drop/rise for the panels. The main house panel is 200A and there are plenty of spare spaces. I’m planning a 90A breaker in the main panel, feeding either 2-2-2-4 MHF (or separate USE-2 2ga conductors depending on cost) from the house to the shop and terminating in a 100A 24 space main breaker panel used as a subpanel. The subpanel will be grounded with 2 ~ 8ft driven rods. Separated neutral & ground bus in the subpanel.
Panel https://www.lowes.com/pd/Square-D-1...ug-On-Neutral-Load-Center-Value-Pack/50311147
Q1: Feeder to the subpanel be run in orange HDPE roll conduit? My B-I-L works in fiber and can provide the conduit he uses for next to nothing (he'll be trenching and pulling the wire regardless). 2" SDR11 I believe. I'll be running a parallel conduit with fiber as well for internet to the shop also. I know the NEC allows for HDPE conduit in direct burial applications, but I don’t see anything that requires a certain color. I know orange is typically used for telecom, but that’s just industry norms.
Q2: Can I / should I bond the ground to the metal building frame as well? I'm pretty sure I need to by code. If so, what is the proper way to do this? Separate #6 Cu down to one of the anchor bolts?
Branch Circuit Wiring

I've been doing A LOT of reading, on this forum and other sites, and I think I have a good start, but I'd like to get some input on my plans. I'm not un-familiar with electrical codes (permit drawings as part of my job), but the maximum extent of my electrical install knowledge is adding a circuit and wiring for my compressor in the main house garage.
The shop is in Florida, so 2017 NEC still applies. As I said, 24 x 30, 9' eave height metal building (Carolina Carports type), just a one man hobby shop. No electrical on the permit since it was originally going to be a while before I could afford it, but I will be pulling a permit when I do the work. One thing I screwed up on and DIDN'T do was add an UFER prior to the slab being poured. I planned to, spoke to the construction super about it, then the concrete day came & we all forgot about it until it was too late. So here is what I'm planning so far:
Loads:
- 240v compressor (Husky 60 gal, labeled as 3.2HP, but the nameplate just reads “spl”)
- 240v 200A welder
- 240v dust collection (2HP) eventually
- LED lighting (probably 4’ integrated T5 fixtures from Amazon)
- General receptacles
- Gable fan?
- Various wood working tools (table saw / router / bandsaw / planer / sanders)
- MAYBE a 24k mini-split some time down the line (wishful thinking)
The run is about 180 feet including drop/rise for the panels. The main house panel is 200A and there are plenty of spare spaces. I’m planning a 90A breaker in the main panel, feeding either 2-2-2-4 MHF (or separate USE-2 2ga conductors depending on cost) from the house to the shop and terminating in a 100A 24 space main breaker panel used as a subpanel. The subpanel will be grounded with 2 ~ 8ft driven rods. Separated neutral & ground bus in the subpanel.
Panel https://www.lowes.com/pd/Square-D-1...ug-On-Neutral-Load-Center-Value-Pack/50311147
Q1: Feeder to the subpanel be run in orange HDPE roll conduit? My B-I-L works in fiber and can provide the conduit he uses for next to nothing (he'll be trenching and pulling the wire regardless). 2" SDR11 I believe. I'll be running a parallel conduit with fiber as well for internet to the shop also. I know the NEC allows for HDPE conduit in direct burial applications, but I don’t see anything that requires a certain color. I know orange is typically used for telecom, but that’s just industry norms.
Q2: Can I / should I bond the ground to the metal building frame as well? I'm pretty sure I need to by code. If so, what is the proper way to do this? Separate #6 Cu down to one of the anchor bolts?
Branch Circuit Wiring
- 10/2 NM-B on 30A breaker for 3HP compressor. Compressor will be outside and covered so I'll be adding a 30A outdoor fusible disconnect.
- 12/2 on 30A breaker for dust collection
- 8/2 NM-B on 50A breaker for 200A multi-process welder. Maximum input amperage is 36A @ 240V @ 15% duty cycle. I'm counting on (2) 240V welder receptacles, 1 on either side of the shop (only 1 welder) and basing the wire size on the longest run.
- 12/3 NM-B for general 20A receptacle outlets (split wired)
- 14/2 NM-B for lighting circuits