Detached Garage Sub Panel Feeder and Load Questions

jmvar

Active member
Joined
Sep 19, 2010
Messages
38
I have a 750 sq ft detached garage that I had big plans for but I have hit a bit of a hiccup financially so I need to use as it sits right now with out any upgrades for a while.

The original owner that had the garage built and wired used a 60A breaker off the 200A panel in the house. They ran what looks like 8 awg copper wire to the garage to a small panel. It is run in PVC conduit underground and the distance is about 40 ft from the main panel to the sub panel in the garage.

I am trying to figure out what load this can support and see if I can get by for a while before I upgrade it.

Questions:

- I am looking for the gauge on the wire but can't seem to find it. I measured it to have .228" diameter with my calipers and the only identifier I can see on it says " oil and gasoline resistant". My assumption is that it is 8 awg THHW wire from AWG diameter charts I have found and descriptions. Does this sound about right?

- Assuming it is 8 awg THHN wire, it looks like max ampacity is 55 amps. At 80% this would be cut down to 44 amps. Does this sound right?

- I want to run the normal garage tools and some wood working equipment while having the 220 v electric heater (17A) or window AC (5A) unit running. I have a delta dust collector (220v, 6A or 120V, 12A) dewalt planner (15 amps), Miller 211 welder I want to run off 220V, small delta jointer (12A), craftsman 113.** table saw (14A). Assuming the biggest draw would be while the heater is running, dust collector, and the planner, adds up to 44 amps. Lights are 4 8' CFL fixtures but not sure what wattage the bulbs are. Am I cutting it close?
 
To avoid these ads, REGISTER NOW!

klassenl

Well-known member
Joined
Feb 20, 2016
Messages
713
Location
Southern Alberta
My wood shop runs on 30 amps. For a time I had some electric heat but no welder. If you're a one man shop a 60a service will do you 99% of the time - unless of course your welder is huge, then you're screwed.
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,660
Location
Austin, TX
> 80% this would be cut down to 44 amps. Does this sound right?

That's "full draw" continuous - yes. As it's on a 60, you're looking at 80% of that, 48 amps continuous draw before something flips.


60A, in my experience, is more than enough for a 750 sqft garage. I have a 2400 sqft garage, it's running on a 90A circuit. Hot tub, refrigerator, 50A RV outlets, 4 tons of AC, all sorts of stuff.

What will get you is electric heat - that might kick you over if you're up north and running a big electric heater to keep the place warm. I avoided that by using propane on any appliance that needs to heat things fast (tankless hot water, dryer, etc).
 
OP
J

jmvar

Active member
Joined
Sep 19, 2010
Messages
38
What will get you is electric heat - that might kick you over if you're up north and running a big electric heater to keep the place warm. I avoided that by using propane on any appliance that needs to heat things fast (tankless hot water, dryer, etc).

I will climb up and check the label on the electric heater.

What about my assumption that I have 8awg THHW wire? I measured it to have .228" diameter with my calipers and the only identifier I can see on it says " oil and gasoline resistant". My assumption is that it is 8 awg THHW wire from AWG diameter charts I have found and descriptions. Does this sound about right?
 

nafterclifen

Well-known member
Joined
Nov 22, 2014
Messages
525
Location
Poconos, PA
What about my assumption that I have 8awg THHW wire? I measured it to have .228" diameter with my calipers and the only identifier I can see on it says " oil and gasoline resistant". My assumption is that it is 8 awg THHW wire from AWG diameter charts I have found and descriptions. Does this sound about right?

You can use this table as a guide to size your wire. Count the number of wires in the strand and measure it.

http://www.nehringwire.com/stranded-wire-gauge-table/
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
#8 Cu THHN/THWN is 50A, not 55A. The max temp you can use is 75 deg C.

The .228 is about right for #8 THHN.
 
Last edited:
OP
J

jmvar

Active member
Joined
Sep 19, 2010
Messages
38
#8 Cu THHN/THWN is 50A, not 55A. The max temp you can use is 75 deg C.

The .228 is about right for #8 THHN.

Thanks, good to know.

So looking at the wiring in the panel it looks like the ground and the neutral are not bonded. From what I read, this is a good thing. However, I don't see a ground rod anywhere like I do by the panel for the house.

Can you guys look at this setup and see anything I need to address?
 

Attachments

  • IMG_20190831_120726871.jpg
    IMG_20190831_120726871.jpg
    107.8 KB · Views: 88
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
In addition to the comments in post number eight the neutral has white tape on it, that is only allowed with 4 AWG and larger conductors, with 6 AWG and smaller the marking must be continuous it’s minor but still a code violation.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
Also one of the 15a breakers is double tapped. Move a white wire over and add another 15a breaker.

Not a problem with SQ D QO or HOM breakers they are listed for two conductors.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
There's no main breaker so the panel is limited to 6 "handle throws".
(Edit) If there isn't 2 ground rods wired to the equipment ground bus in the panel, there should be
 
Last edited:

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
In addition to the comments in post number eight the neutral has white tape on it, that is only allowed with 4 AWG and larger conductors, with 6 AWG and smaller the marking must be continuous it’s minor but still a code violation.
Based on the look of that panel, it's installation likely preceeded the code change limiting taping to #4 and larger. I'm pretty sure it was allowed to tape any size neutral back in the 80's, maybe 90's. If that's not the case, it was at least a rule that nobody I worked with ever followed back then.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Continuous is 3 hrs or more. It should have the breaker changed to 50. Having a small welder is an asset here, you may never need more than that or changing heater to gas may be cheaper than changing electric?
 