Hi all,
Pulling electricity to detached garage. Buried conduit stubbed out adjacent to garage siding, but offset about 8". (So the far edge of the conduit stub is 8" away from the garage siding.) Plan to run conduit up the wall to a disconnect switch and then carry the conduit into the garage.

So how do I get the conduit from the stubout to lay against the siding?
1. ) LB to LR back to back and then up the siding?
2) 8" box with the stub going in up from one bottom edge and the disconnect conduit exiting the top but offset by the 8"?
3) Digout the stub and add in 6" to get the stub directly adjacent to the siding?
I'm open to suggestions.

The driving issue is the need for an external disconnect. City is on the 2022 CA cycle, which is based on the 2020 NEC.
Thanks,
Murray
 
To avoid these ads, REGISTER NOW!
OP
M

mdr

Active member
Joined
Jun 10, 2009
Messages
40
Location
Bay Area, CA
Here's a simple sketchup. Perspective makes it look wonky. 1.5" conduit stubbed out of ground. About 8" from wall. Would have preferred it directly adjacent to wall.
Apparently, current NEC requires exterior disconnect for service entrance, feeder requirement is less clear. In older cycles, I would have just used a 90 LL, penetrated the wall with conduit, run conduit to interior panel. Not clear whether that is still allowed, so was going to put disconnect on exterior wall and then penetrate from there.
Screen Shot 2024-07-11 at 12.43.59 PM.png
 
To avoid these ads, REGISTER NOW!
OP
M

mdr

Active member
Joined
Jun 10, 2009
Messages
40
Location
Bay Area, CA
Thanks again.
Another question for Sparky - does the disconnect have to be immediately (or as soon as feasible) after the conduit passes through the wall? Do I have to have the panel (with disconnects) at the point of penetration, or can I run conduit and have the panel in a location further from the wall penetration?
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,967
Location
Central Iowa
Thanks again.
Another question for Sparky - does the disconnect have to be immediately (or as soon as feasible) after the conduit passes through the wall? Do I have to have the panel (with disconnects) at the point of penetration, or can I run conduit and have the panel in a location further from the wall penetration?


It's supposed to be asap after it enters the building and a main breaker panel is the easiest and most cost effective way to do it. If that isn't feasible, you could use the exterior disconnect and do whatever you want to inside.
 