Detached Garage wiring from meter

gamitch11

Member
Joined
Feb 12, 2015
Messages
9
I want to run electrical to my detached garage. I want to come off of the meter (not the service panel in the house) to a 125 amp breaker box in the garage with a 125 amp main breaker.

Can this be done by running 3 wires (all #2 copper)?
3 wires = two hots and a neutral from the meter. Then drive two grounding rods at the garage for the grounds at least 6 feet apart and connected with #6 copper wire.

Can I just run the 3 wires?

Thanks for the help.
gamitch
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
I want to run electrical to my detached garage. I want to come off of the meter (not the service panel in the house) to a 125 amp breaker box in the garage with a 125 amp main breaker.

Can this be done by running 3 wires (all #2 copper)?
3 wires = two hots and a neutral from the meter. Then drive two grounding rods at the garage for the grounds at least 6 feet apart and connected with #6 copper wire.

Can I just run the 3 wires?

Thanks for the help.
gamitch

Does your meter have a disconnect or is it just a meter?

If so, it would need to have dual lugs.

What size service do u have?

What electric loads do u have?
 
OP
G

gamitch11

Member
Joined
Feb 12, 2015
Messages
9
Does your meter have a disconnect or is it just a meter?
No, no disconnect. I would have an electrician or OG&E to make the connection.

If so, it would need to have dual lugs.
If no lugs, what would be my options?

What size service do u have? 400 Amp

What electric loads do u have? Right now, for the garage, not much. A 220v compressor. I want to add a window air conditioner and would like to buy a welder. I think the 125 amp would be more than I will need for the garage.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Most 400amp meter pans have dual lugs.

Regardless i would not want that much unfused wire on my property.

And what i meant by what loads do u have is what loads do u have in the house? Range, heater, AC, dryer, etc etc...

How big is the house?
 

MEngineer

Well-known member
Joined
Apr 13, 2015
Messages
345
Location
Everett, Wa
I think you will need at minimum 1/0 copper or 2/0 aluminum.

You can "tap" into your existing feeds that exit your meter and go to your main panel.

Use a fitting like the option below.

I am currently doing this myself. I have 4/0 aluminum supplying my 200 amp panel and then 2/0 aluminum supplying my 150 amp panel using the connectors below.
https://m.platt.com/platt-electric-...ng/Ilsco/IPC-4-0-2-0/Products.aspx?pid=708303
 
OP
G

gamitch11

Member
Joined
Feb 12, 2015
Messages
9
Most 400amp meter pans have dual lugs.

Regardless i would not want that much unfused wire on my property.

And what i meant by what loads do u have is what loads do u have in the house? Range, heater, AC, dryer, etc etc...

How big is the house?
By 'dual lugs' do you mean that there might be a place to attach wires or are they already used up by two sets of wires coming from the transformer to my meter?


The electrician could install a fused box (or breaker box) at the meter, then I could run my wires from that box to a garage sub panel?

House is 2600 sq.ft. Total Electric - 2 ac units, 2 heaters, 2 hot water heaters, range, oven, dryer, well pump. I don't know what load would come from the meter to the house. My OG&E bill shows a maximum usage of 14652 watts during a 15 minute interval. I know that won't accurately show an instant load.
 
OP
G

gamitch11

Member
Joined
Feb 12, 2015
Messages
9
I think you will need at minimum 1/0 copper or 2/0 aluminum.

You can "tap" into your existing feeds that exit your meter and go to your main panel.

Use a fitting like the option below.

I am currently doing this myself. I have 4/0 aluminum supplying my 200 amp panel and then 2/0 aluminum supplying my 150 amp panel using the connectors below.
https://m.platt.com/platt-electric-...ng/Ilsco/IPC-4-0-2-0/Products.aspx?pid=708303
Thanks MEngineer. Won't #2 copper handle the 125 amp?

I'll keep the taps in mind and suggest them to my electrician.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
IMHO - You'd need to ask OG&E. I did it here with AEPs blessing and the co-op did it for my 100A shop panel. That is, stack the wire under a single lug - customer side of the meter base.
 
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,126
Location
SE MI
Most 400amp meter pans have dual lugs.
400A is very unusual for residential. 200A is considered "large"

Regardless i would not want that much unfused wire on my property.

ABSOLUTELY ! If some one accidentally digs up or hits YOUR unfused line line they are pretty much dead, unless they are "blown off" the line !

Get an outdoor rated, 2 circuit, 400A rated fuse or breaker panel. 400A rating will cost you some serious $$$ so make sure that is what you need.


FYI, for the loads you listed in the garage, 60A should be adequate.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,126
Location
SE MI
IMHO - You'd need to ask OG&E. I did it here with AEPs blessing and the co-op did it for my 100A shop panel. That is, stack the wire under a single lug - customer side of the meter base.

That is pretty unusual ! They do make single to dual lug adapters.

Glad to hear you went through the proper channels. Keep your paper work because some home inspector might cry "foul" when you sell the place.
 

Dragfluid

ALLIANCE MEMBER
Joined
Sep 15, 2013
Messages
17,512
Location
Pillager, MN
When I ran my 4/0 to the shed, I bought some dual lugs from the elec supply house for a few bucks each. Bolted them in the disconnect box and away we went.
 

Gerald O

Well-known member
Joined
Mar 5, 2013
Messages
1,884
Location
NC
Here's what I ended up doing: 320/400 amp dual lug meter base feeding two disconnect boxes each with 150 amp main disconnects. One feeds the house load center, and the other feeds the garage load center through 4/0-4/0-4/0-2/0 AL SER cable. There are two ground rods at the meter, and the garage has a UFER ground in the foundation.
 

Attachments

  • attachment.jpg
    attachment.jpg
    13.9 KB · Views: 106
  • attachment-1.jpg
    attachment-1.jpg
    14.1 KB · Views: 81
  • attachment-2~2.jpg
    attachment-2~2.jpg
    36.4 KB · Views: 95
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Here's what I ended up doing: 320/400 amp dual lug meter base feeding two disconnect boxes each with 150 amp main disconnects. One feeds the house load center, and the other feeds the garage load center through 4/0-4/0-4/0-2/0 AL SER cable. There are two ground rods at the meter, and the garage has a UFER ground in the foundation.

I hope I'm misunderstanding this, but you have SER serving a detached garage it better not be run underground, even if conduit?
 

Gerald O

Well-known member
Joined
Mar 5, 2013
Messages
1,884
Location
NC
I hope I'm misunderstanding this, but you have SER serving a detached garage it better not be run underground, even if conduit?

It's actually attached by a small 'mudroom' and the SER routes through the crawlspace. So that part would not apply to the OP's situation. He'd need a buryable cable for his detached building.
 
Last edited: