Diagonal braces

bagged89s10

Well-known member
Joined
Mar 13, 2005
Messages
4,607
Location
CT
I just had this 35x24 garage built. 10ft high walls and 24ft span trusses. yesterday I noticed if I grab the gable wall and try hard to shake it that I can shake the garage slightly. I think I need diagonal braces on the long 35ft wall and maybe one on each end of the wall with the doors The inspector didn’t say anything.

what should i use to add the braces? 1x4 on the face of the studs seems like the easiest? I do plan to insulate and drywall the garage so I would have to add a bunch of furring strips.

how long do I make them?

how many do I need?

which direction and angle is best?

thanks for your help.
 

Attachments

  • 24954308-66AA-4068-8807-D40FEF36A59F.jpeg
    24954308-66AA-4068-8807-D40FEF36A59F.jpeg
    343.3 KB · Views: 210
  • C1AACA33-4007-44C9-8992-D7582A04AA6D.jpeg
    C1AACA33-4007-44C9-8992-D7582A04AA6D.jpeg
    279.2 KB · Views: 210
  • B4086586-261A-4285-B28C-2ED191B77BE9.jpeg
    B4086586-261A-4285-B28C-2ED191B77BE9.jpeg
    613 KB · Views: 207
To avoid these ads, REGISTER NOW!

nmk_61802

Well-known member
Joined
Mar 6, 2008
Messages
965
Location
Central IL
Are those scissor trusses? If so that end wall should have been framed full height for a few studs, no hinge joint at the top plate.


I don't see angular bracing at the end trusses? This is the min bracing that should have been followed unless you had a different packet with the trusses:


There is a min of 4' required on each corner at the doors, other wise portal framing is needed. Do you have that? I would guess each of these issues contributes to the movement your are seeing.

Also if the bear min code is followed, interior drywall or sheeting is also needed to fully stiffen building.
 
Last edited:
OP
B

bagged89s10

Well-known member
Joined
Mar 13, 2005
Messages
4,607
Location
CT
Are those scissor trusses? If so that end wall should have been framed full height for a few studs, no hinge joint at the top plate.


I don't see angular bracing at the end trusses? This is the min bracing that should have been followed unless you had a different packet with the trusses:


There is a min of 4' required on each corner at the doors, other wise portal framing is needed. Do you have that? I would guess each of these issues contributes to the movement your are seeing.

Also if the bear min code is followed, interior drywall or sheeting is also needed to fully stiffen building.
The truss drawings only call for bracing at the top and bottom chords. The top says structural sheathing or purlins at X spacing. We used 5/8” structural sheathing. Bottom chord says rigid ceiling or 10ft on center purlins. We have 10ft on center bracing. The framers nailed 2x4s for bracing. Maybe how and where they nailed these this isn’t sufficient. It doesn’t say anything about cross bracing or diagonal bracing.

I do plan to nail 1x3 furring strips and then drywall to the ceiling but wasn’t planning on it until either the winter or next year.
 
OP
B

bagged89s10

Well-known member
Joined
Mar 13, 2005
Messages
4,607
Location
CT
Are those scissor trusses? If so that end wall should have been framed full height for a few studs, no hinge joint at the top plate.


I don't see angular bracing at the end trusses? This is the min bracing that should have been followed unless you had a different packet with the trusses:


There is a min of 4' required on each corner at the doors, other wise portal framing is needed. Do you have that? I would guess each of these issues contributes to the movement your are seeing.

Also if the bear min code is followed, interior drywall or sheeting is also needed to fully stiffen building.
What do you mean 4’ at each corner at the doors? Also what is portal framing?
 

nmk_61802

Well-known member
Joined
Mar 6, 2008
Messages
965
Location
Central IL
4’ from jamb to building corner


For the truss bracing do you have a stiff back and angle brace back to second truss at each end truss. That was the angular brace I was questioning and is shown on sheet B3/ third column
 
Last edited:

firebirdparts

Well-known member
Joined
Jun 8, 2016
Messages
10,594
Location
Kingsport, TN
So the best direction to brace, to get it out of the way, is flat through the attic. The roof is pretty rigid, and that is already doing a lot, but if you're not satisfied, you can always do more by running 2 by 4's diagonally through the attic. Corner to Corner probably makes the most sense. If you sheeted the ceiling with something solid (not saying you want to) that is even better.

That creates a situation where the entire top of the building has to stay exactly rectangular and if any of it moves, it all has to move.

Then, if you have rigid walls, that rectangle in the air can't move either, because the ridge walls and the earth don't allow it to move. If your walls are fully sheeted, they should be rigid, but you can put diagonal sheeting anywhere on the wall, no harm done.

Having done that, you can still bend the wall in the weak direction, but you can't brace against that and really you shouldn't.
 

WNYflyer

Well-known member
Joined
Sep 13, 2009
Messages
2,119
Location
Lockport, NY
Are those scissor trusses? If so that end wall should have been framed full height for a few studs, no hinge joint at the top plate.

^^^ Are the gable end walls ballooned framed? in other words do the studs run continuously from sole plate to the roof deck such there is no hinge at ceiling level? In reality the way a gable end should be constructed if lacking a diaphragm or some type of horizontal bracing at the ceiling level which would brace a hinged joint.
That being said there are all kinds of garages out there built with a hinge joint that haven’t fallen down but I bet a good many of them move, shake, rattle and roll in a good wind. Often even more of a problem in gable walls with openings due to less structure.
 

JAB82

Member
Joined
Apr 23, 2018
Messages
9
Once you put the ceiling in it will not shake if you cant do it now that's ok it is plenty strong with the roof sheathing if you still want to do something before you install the ceiling you can install 2x4 on the top of the bottom cord of the truss at a angle from the gables to the 35 foot walls make them as long as you can and if you need to use 2 2x4's you need to lap them next to each other by 2 trusses just not on one cord end to end. Another thing you can do is install plywood on the soffit before your soffit material of choice just remember to cut openings in it for venting if you are going to insulate and heat the building down the road this will add a extra horizontal brace to the 35 foot long wall
 

strutaeng

Well-known member
Joined
Dec 12, 2011
Messages
2,262
Location
Dallas, TX
Yeah, either brace with 2x4 every 6-8' on top of the bottom chord (perpendicular) to the gable wall, if you plan to add a ceiling on the bottom chord of the trusses. Or you can add "kickers" from gable wall to the roof deck. May be a little difficult to get between the webs of the trusses. Or run gable trusses full height (too late for that.)
 
To avoid these ads, REGISTER NOW!
OP
B

bagged89s10

Well-known member
Joined
Mar 13, 2005
Messages
4,607
Location
CT
Once you put the ceiling in it will not shake if you cant do it now that's ok it is plenty strong with the roof sheathing if you still want to do something before you install the ceiling you can install 2x4 on the top of the bottom cord of the truss at a angle from the gables to the 35 foot walls make them as long as you can and if you need to use 2 2x4's you need to lap them next to each other by 2 trusses just not on one cord end to end. Another thing you can do is install plywood on the soffit before your soffit material of choice just remember to cut openings in it for venting if you are going to insulate and heat the building down the road this will add a extra horizontal brace to the 35 foot long wall

I think I’ll add some diagonals to the bottom chords and I’ll inspect how well the other braces are attached to the bottom chords before I insulate and drywall the ceiling.
 

mcbane

Well-known member
Joined
Jul 23, 2017
Messages
794
Location
California
I just had this 35x24 garage built. 10ft high walls and 24ft span trusses. yesterday I noticed if I grab the gable wall and try hard to shake it that I can shake the garage slightly. I think I need diagonal braces on the long 35ft wall and maybe one on each end of the wall with the doors The inspector didn’t say anything.

what should i use to add the braces? 1x4 on the face of the studs seems like the easiest? I do plan to insulate and drywall the garage so I would have to add a bunch of furring strips.

how long do I make them?

how many do I need?

which direction and angle is best?

thanks for your help.
I am an engineer but not in your state. Your observations sound like there was a snafu in construction, and you shouldn’t be doing as hoc corrective action based on details you get online. Contact the person who designed your structure and ask what details should have been constructed to resist side sway under design forces and also uplift during wind storms. Ideally ask that person to make a site visit so you can get clear corrective action items for your contractor.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,932
Location
Coronado, CA
Without good bracing a building is like stack of dominoes; and I am not referring to pizza. Wind load and seismic activity have collapsed many buildings that somebody thought was "Good enough"
 

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
I just had this 35x24 garage built. 10ft high walls and 24ft span trusses. yesterday I noticed if I grab the gable wall and try hard to shake it that I can shake the garage slightly. I think I need diagonal braces on the long 35ft wall and maybe one on each end of the wall with the doors The inspector didn’t say anything.

what should i use to add the braces? 1x4 on the face of the studs seems like the easiest? I do plan to insulate and drywall the garage so I would have to add a bunch of furring strips.

how long do I make them?

how many do I need?

which direction and angle is best?

thanks for your help.

That's an awesome building. I agree with @mcbane, get the Engineer who designed the building to come out and review the building verses the actual construction.

Food for thought: Any revisions you do on your own may end up biting you in the **** if there is ever an issue with the building. By making modifications, you may also be taking on the liability.

When I had my pole barn built I was on site during the entire construction. There were numerous items where the on site guys were not going to following the engineered drawings. Each time I pointed this out, showed them the drawing, and they then proceeded per the drawing.
 

mrobins297aaa

Well-known member
Joined
Sep 20, 2010
Messages
3,283
Location
south east michigan
on the gable ends those studs need to be continuous from the floor plate to the bottom of what ever kind of truss you have there. if not you'll have a hinge joint at the top plate that you'll never get out with bracing.
 

nmk_61802

Well-known member
Joined
Mar 6, 2008
Messages
965
Location
Central IL
Shouldn't the blocking in the stud cavities be positioned horizontal and not vertical?

Don't think that is fire blocking, but code required nailers at each sheating seam. I believe either orientation is sufficient to comply with code.
 

Toolfool

Well-known member
Joined
Aug 22, 2011
Messages
4,981
Location
Tallahassee, FL
Don't think that is fire blocking, but code required nailers at each sheating seam. I believe either orientation is sufficient to comply with code.
This is for shear. Hopefully, the framers have nailed off the plywood to these blocks as well as the studs.
 

Tman

Well-known member
Joined
Jan 29, 2006
Messages
543
Location
Black Hills of South Dakota
If it is determined you need cross bracing on the walls, you can get formed metal bracing strips won't interfere with any interior sheathing: https://www.homedepot.com/p/Simpson...all-Bracing-with-Rolled-Edges-TWB12/100375133
I have used these a lot, they do their job.

If it is determined you need cross bracing on the walls, you can get formed metal bracing strips won't interfere with any interior sheathing: https://www.homedepot.com/p/Simpson...all-Bracing-with-Rolled-Edges-TWB12/100375133
 
To avoid these ads, REGISTER NOW!
Top Bottom