I'm preparing to install a farenheat 5000 watt heater in my garage. I ran 8/2 nm wire thinking it was fine. I downloaded the manual for the heater and it says to use wire rated for at least 75deg. I believe NM is only 60? Did I just screw up?
 
To avoid these ads, REGISTER NOW!

n8n

Well-known member
Joined
Mar 11, 2014
Messages
3,607
Location
Curtis Bay, MD
Any current production NM is actually NM-B which is 90C rated. Have a look at the jacket on your cable.
 
OP
O

oba97

Active member
Joined
Feb 2, 2014
Messages
36
I'll take a peak, I just bought it yesterday so should be fine. Now my concern is I have it connected to a line that was installed with the house in 1978. It white ettcoflex 8/3 nm.
 

n8n

Well-known member
Joined
Mar 11, 2014
Messages
3,607
Location
Curtis Bay, MD
well the old stuff is only NM, but I'm guessing the instructions are likely only concerned with the wire immediately connected to the device, not the entire length of the run feeding it. Now if you were bringing your entire house up to current code you'd have to repull the whole thing with NM-B but if you do not anticipate high ambient temperatures near it and the insulation appears to be in good condition, you should be fine with what you have.
 
To avoid these ads, REGISTER NOW!
OP
O

oba97

Active member
Joined
Feb 2, 2014
Messages
36
Ok, thanks for the info. Is the main issue I could have is melting the insulation? Just wondering what I should look for upon start-up.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
For a 5000 watt heater you should only need #10. Did the instructions say to use #8? The insulation on NM is fine for 75 deg C. The NEC just limits the amp sizing for NM to 60 deg C.
 
OP
O

oba97

Active member
Joined
Feb 2, 2014
Messages
36
I already had half a run or 8guage from an old stove. I just tied into that to finish the run vs running 75' of 10 guage.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
The wire connecting directly to the heater must meet this temperature rating. The branch circuit can be lower.
 