My HVAC consists of a boiler connected to in floor heat as well as a fan coil unit that also has an A/C coil in it. A few years ago I had a "pro" service the system and the following summer I noticed that the boiler was running when the A/C was on. Strange... I don't remember it doing that. I didn't know what was up and ended up wiring in another switch to just turn off the boiler in the summer.
So now I'm thinking about adding another water zone to drive an indirect water heater. It took me a couple of weeks off and on to learn some of the jargon (forgive me if I use the wrong words) and go through the rats nest of wires and now I think I found the problem.
The attached picture is representative of the wires I traced. I left off a lot of the zone wires as well as the contactor wires for the A/C.
So if I understand this all, I think the relays are set up so that the middle relay will run the low speed fan circuit if the thermostat energizes the green wire. I couldn't see the relay terminal layouts and I'm not sure what terminals a and b are (assume 2 and 5) but I believe 4 and "a" are connected as N/O and that when the coil gets energized that would cause the fan to run at low speed.
Next I look at the DPDT and I see that the 2 terminal is the normally closed circuit and that the 3 terminal is the normally open. So I assume this relay is supposed to energize when A/C is on and cause the high speed fan to run while removing power from the middle relay so that the low speed fan is not energized.
OK, this sounds good but wait... look at how the DPDT relay's coil is energized???? The cool (blue, should be yellow) and heat (white) are on opposite sides of the coil (WTF??). I see the transformer is also energizing one side of the coil but white is on the other side of that (WTF!!!!) From my little bit of understanding shouldn't the transformer be on one side of the coil and the cool (blue, normally yellow) be on the other side of the coil to energize this relay for A/C????
Hmm... so not shown is the outside contactor. It is connected to the red transformer wire and the other side of the coil in the relay. I think it is the outside contactor and the blue that are energizing the coil but I haven't measured that yet.
I haven't confirmed but it looks to me like the white being connected to the DPDT relay coil is likely energizing the coil and causing my fan to run at high speed for heat and cool but again, I haven't verified this just yet.
Finally, the zone valve is getting energized whenever there is 24v going through the coil. Since it appears to me that the coil gets energized by the white wire as well as the outside contactor that whenever the thermostat calls for either heat or cool that the zone valve will get energized, and of course, that will close the contacts for the TT connections to the boiler and my boiler runs. Is this what is happening?????
It really seems to me that the pro messed up and should have connected the brown from the transformer to one end of the DPDT relay coil and the blue (should have been yellow) cool circuit from the thermostat to the other end of the coil. Then to turn on the boiler for HEATING ONLY he should have connected one of the yellow wires to the brown at the coil as it is in the picture, white to terminal 4, and the other yellow to terminal 5. In this way the zone valve would be energized whenever the heat circuit (white) is energized and the cool circuit (coil not energized) isn't. See the proposed wiring picture.
Let me know if I'm on track here. Next up is a discussion of how I plan to clean up the rats next with a zone valve controller that I can then also use to create a priority zone for a new indirect water heater. I'd also like to run the fan coil unit off the zone valve controller but I need to work out transformer issues. I'll leave that discussion to another thread.
So now I'm thinking about adding another water zone to drive an indirect water heater. It took me a couple of weeks off and on to learn some of the jargon (forgive me if I use the wrong words) and go through the rats nest of wires and now I think I found the problem.
The attached picture is representative of the wires I traced. I left off a lot of the zone wires as well as the contactor wires for the A/C.
So if I understand this all, I think the relays are set up so that the middle relay will run the low speed fan circuit if the thermostat energizes the green wire. I couldn't see the relay terminal layouts and I'm not sure what terminals a and b are (assume 2 and 5) but I believe 4 and "a" are connected as N/O and that when the coil gets energized that would cause the fan to run at low speed.
Next I look at the DPDT and I see that the 2 terminal is the normally closed circuit and that the 3 terminal is the normally open. So I assume this relay is supposed to energize when A/C is on and cause the high speed fan to run while removing power from the middle relay so that the low speed fan is not energized.
OK, this sounds good but wait... look at how the DPDT relay's coil is energized???? The cool (blue, should be yellow) and heat (white) are on opposite sides of the coil (WTF??). I see the transformer is also energizing one side of the coil but white is on the other side of that (WTF!!!!) From my little bit of understanding shouldn't the transformer be on one side of the coil and the cool (blue, normally yellow) be on the other side of the coil to energize this relay for A/C????
Hmm... so not shown is the outside contactor. It is connected to the red transformer wire and the other side of the coil in the relay. I think it is the outside contactor and the blue that are energizing the coil but I haven't measured that yet.
I haven't confirmed but it looks to me like the white being connected to the DPDT relay coil is likely energizing the coil and causing my fan to run at high speed for heat and cool but again, I haven't verified this just yet.
Finally, the zone valve is getting energized whenever there is 24v going through the coil. Since it appears to me that the coil gets energized by the white wire as well as the outside contactor that whenever the thermostat calls for either heat or cool that the zone valve will get energized, and of course, that will close the contacts for the TT connections to the boiler and my boiler runs. Is this what is happening?????
It really seems to me that the pro messed up and should have connected the brown from the transformer to one end of the DPDT relay coil and the blue (should have been yellow) cool circuit from the thermostat to the other end of the coil. Then to turn on the boiler for HEATING ONLY he should have connected one of the yellow wires to the brown at the coil as it is in the picture, white to terminal 4, and the other yellow to terminal 5. In this way the zone valve would be energized whenever the heat circuit (white) is energized and the cool circuit (coil not energized) isn't. See the proposed wiring picture.
Let me know if I'm on track here. Next up is a discussion of how I plan to clean up the rats next with a zone valve controller that I can then also use to create a priority zone for a new indirect water heater. I'd also like to run the fan coil unit off the zone valve controller but I need to work out transformer issues. I'll leave that discussion to another thread.