Different circuit sizes in the same gang box

jjscott

Well-known member
Joined
Aug 9, 2014
Messages
114
I have an existing single gang box with a 20 amp outlet in it (12/2 wire) and want to replace it with a dual gang box so I can add a 15 amp light switch (14/2 wire) to it.

It is my understanding that this would not be a code violation or cause any issues. Can you confirm this is correct?

I realize that the hot & neutrals for both circuits can't be tied together, but someone mentioned that the grounds from both circuits should be tied together. Is this true?

If so, how would this work? Wirenut the grounds from both circuits and two pigtails together and then have one pigtail wired to the ground terminal on the 20 amp outlet and the other pigtail wired to the ground terminal on the 15 amp light switch?
 
To avoid these ads, REGISTER NOW!

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,771
Location
Southern Oregon
You're fine. Multiple circuits in the same box are OK. Just like you said, keep the hots and neutrals from each circuit separated, join the grounds, ground the box if its metal.
 
OP
J

jjscott

Well-known member
Joined
Aug 9, 2014
Messages
114
You're fine. Multiple circuits in the same box are OK. Just like you said, keep the hots and neutrals from each circuit separated, join the grounds, ground the box if its metal.

Is it a requirement to tie the grounds from both circuits together or just best practice?
 