I am direct burying wire to the shop. Have trenched 24 inches and have rocks in the dirt. Does it hurt to put those rocks back in the trench. Should I fill with black dirt first? 4/0,4/0,2/0,4 mobile home urd is the wire. Trench bends do not make conduit easy.
 
Last edited:
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Use sand or clean dirt around the wires. Rocks will get up against the wires and eventually eat thru the insulation. I'd put at least 6 inches or so of clean dirt/sand on top before putting the rocky soil back in.

Charles
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Your wire is either Mobile Home Feeder (MHF) or it's URD also know as UD. There's a difference as to where MHF can be installed vs. URD.
 

malibu101

Well-known member
Joined
Jul 1, 2005
Messages
3,908
Location
Walnutport PA
Around here we use "screenings". It is the fines that are leftover from crushing stone.
They are fine so they will not hurt what they are covering, they level out relatively easy, compact easily, and if in the future you dig around it you will see the different material covering the wire/pipe before ripping it out.

Lay cable trace marker ribbon (or even caution tape if it's all you have) a few inches below finish grade so again future diggers will see it and know there is something below.
 

arrowhead

Well-known member
Joined
Dec 11, 2008
Messages
681
Location
Stillwater, NY
Well since you using direct bury cable anyway, why not just use conduit for the straight lengths and no fittings? That way you only have to worry about the exposed cable around the bends being protected by sifted dirt, the rest will be protected by the conduit.
 

joe_padavano

Well-known member
Joined
Feb 26, 2011
Messages
1,788
Location
Northern VA
I still struggle with the concept of paying for direct burial cable then also paying for conduit. Yes, I use conduit where required, like under road ways, but otherwise, I just put the wire in the trench. Stone dust under and over the wire solves the rock problem.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
NO WAY I'd use direct bury service cable in anything but sandy soil, or bedded in a lot of fine material.

If the trench is that bad they should have dug it better.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
I still struggle with the concept of paying for direct burial cable then also paying for conduit. Yes, I use conduit where required, like under road ways, but otherwise, I just put the wire in the trench. Stone dust under and over the wire solves the rock problem.
But you're OK with paying for the stone dust and the labor and machines to spread it??? :lol:

How much "extra" do you pay for DB cable??? I use URD in conduit all the time. It's easier and the same price as individual conductors, and I don't have to mess with stone dust unless the soil is really bad.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Well since you using direct bury cable anyway, why not just use conduit for the straight lengths and no fittings? That way you only have to worry about the exposed cable around the bends being protected by sifted dirt, the rest will be protected by the conduit.

Thats makes no sense! Why would someone go through all that trouble just to half *** the conduit? If im using conduit Im gonna glue it together fittings and all.

Or a 200A service. ;)

My point exactly. 200a is A LOT of equipment! Probably overkill!
 

arrowhead

Well-known member
Joined
Dec 11, 2008
Messages
681
Location
Stillwater, NY
Thats makes no sense! Why would someone go through all that trouble just to half *** the conduit? If im using conduit Im gonna glue it together fittings and all.


Well if you read his posts, the trench layout makes putting fittings on the conduit next to impossible. He's using direct bury cable anyway, so slipping straight lengths of conduit where possible is just some extra insurance against chaffing with the poor back fill material he has. Why is that half assed?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Well if you read his posts, the trench layout makes putting fittings on the conduit next to impossible. He's using direct bury cable anyway, so slipping straight lengths of conduit where possible is just some extra insurance against chaffing with the poor back fill material he has. Why is that half assed?

Should have made the trench better! And conduit is designed to be a complete system. Just think if that cable ever has to be replaced. If the conduit is complete then all u have to do is pull out the old and pull in the new. The way he suggests, he would have to redig the trench. And URD does fail especially with rocks.
 
To avoid these ads, REGISTER NOW!

arrowhead

Well-known member
Joined
Dec 11, 2008
Messages
681
Location
Stillwater, NY
Should have made the trench better! And conduit is designed to be a complete system. Just think if that cable ever has to be replaced. If the conduit is complete then all u have to do is pull out the old and pull in the new. The way he suggests, he would have to redig the trench. And URD does fail especially with rocks.

That's great Monday morning quarterbacking and all, but your not really helping him solve the problem. He asked if all the soil needs to be sifted and I gave him an alternate solution so he could work with what he had.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
No rocks. Friends just had their house floor jackhammered to fix a pipe leak. They have been there 20+ years at least, cause was a bitty rock that was in the sand pad under the concrete floor resting against the pipe. Took a long time, but it eventually drilled a hole in the pipe.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Loook at the wire closely. If it has a yellow or yellow striped neutral, it is almost certainly URD and NOT MHF. MHF will have a white stripe neutral.

USE is forbidden by code from being used above ground for any reason except to junction to another type of cable, and is never allowed inside a building, not even 6 inchs inside. The wire must be marked with other markings such as the RHW/RHH. URD is usually dual rated as USE, but NOT rated otherwise (see Southwire spec sheet for UD)

MHF is almost identical looking wire, but has a white stripe neutral, and can be run inside a building (in conduit or proper raceway) in addition to being direct buried or buried in conduit. MHF is also multi-rated as USE-2/RHH/RHW

attachment.php


Charles
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I've repaired A LOT of DB aluminum cable.

Installing DB cable in rocky soil without conduit is a mistake. It only takes one little nick in the cable....
 

joe_padavano

Well-known member
Joined
Feb 26, 2011
Messages
1,788
Location
Northern VA
But you're OK with paying for the stone dust and the labor and machines to spread it??? :lol:

A load of stone dust isn't very expensive and the "labor and machines to spread it" are me and my tractor. MUCH faster and easier than laying out and gluing conduit, then dragging the cable through it. I actually did exactly this with 4/0-4/0-4/0-2/0 where the direct burial had to run under a gravel road. I only needed to run about 50 ft of conduit, and it was a ROYAL PAIN. The remaining 400 ft went MUCH faster (and yes, the 4/0 was for voltage drop over that long run).
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
A load of stone dust isn't very expensive and the "labor and machines to spread it" are me and my tractor.
Then IMO your opinion is not very valid to someone either DIYing this or paying to have it done. Not everyone has cheap access to material and obviously not everyone has a machine.
For a typical electrical contractor it is far easier and safer to go the conduit route.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
Then IMO your opinion is not very valid to someone either DIYing this or paying to have it done. Not everyone has cheap access to material and obviously not everyone has a machine.
For a typical electrical contractor it is far easier and safer to go the conduit route.

Conduit is cheap insurance in my opinion.
 

rburke65

Well-known member
Joined
Nov 10, 2007
Messages
12,349
Location
Canfield, Ohio
Did a direct berial for my neighbor as he didn't want to spend the money for conduit. About 10 years later we were redoing it in conduit as we lost a leg due to rocks I guess. I would do the conduit......And as always.....just my opinion.
 
OP
B

bloomingtonmike

Well-known member
Joined
Dec 1, 2011
Messages
314
Location
Bloomington, IL
I did conduit - you guys scared me. Got it installed the last couple days with the help of my wife and a couple friends. Just finished burying most of it. Need to do the connections at the ends still and install the elbow and conduit and bury at the shop end.

Working on the csst gas line now.
 

kaffine

Well-known member
Joined
Dec 13, 2009
Messages
3,610
Location
Henderson, NV
Put several inches of sand in the bottom before the wire. Put the wire in and cover with sand making sure the wire stays away from the side of the trench. The wire should be surrounded by several inches of sand on all sides. Then any large rocks get removed before backfilling the rest of the way. I would put warning tape on top of the sand and again 6 inches or so below final grade. If I was only going to put one warning it would be the top one. Also draw a map of the run and keep a copy.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
What do you consider a LOT of equipment? Ever been to a techshop/makerspace? I am building my own personal one and own 80% to the machines already.

Eh, just your regular CNC vertical mill, shaper, big giant lathe and stuff. Everybody has those. :lol: Well, they wish. :thumbup:

The main deal is - better do whatever best now, because re-doing it a PITA. It's a big pain to back up or change directions, but really less of a total pain now than later. Nice machines, don't skimp too much on feeding them.

Idea - since you have a giant band saw - use the sand as noted, slice some 2" PCV longways and lay it in the trench, then lay the wire, then sand. Or slice some 3" or 4" and lay the wire in that bedded in sand, cover with the other half. Keeps the rocks out and you'd have something to hit before the wire should you be digging in the area in the future.
 
Last edited:

volleyball

Well-known member
Joined
Aug 29, 2011
Messages
4,127
Location
NY, not NYC
I did conduit - you guys scared me. Got it installed the last couple days with the help of my wife and a couple friends. Just finished burying most of it. Need to do the connections at the ends still and install the elbow and conduit and bury at the shop end.

Working on the csst gas line now.

After the gas line, run some coax and cat 6 cable above the electric and csst.
 