Disable the AUX when on the generator

WaterBoyz

Well-known member
Joined
Nov 16, 2015
Messages
368
Location
Northern VA
My Trane heat pump has the huge meter-spinning toaster coils as AUX heat. The generator is not large enough to power those when the outdoor unit goes into defrost mode. I need to stop the toaster from turning on.

I realize that there will be some amount of chilled air coming from the air handler during the defrost period, which I will have to tolerate.

I plan to install a simple manual toggle switch that disables the toaster ONLY when on the generator. My Ecobee thermostat has been programmed to never turn on the AUX, but I do want to be sure it does not sneak in an AUX call.

Thanks........

The generator is for backup only, so I'm not an off-the-grid lifestyle.

Air Handler wiring diagram.JPG
 
To avoid these ads, REGISTER NOW!

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,622
Location
Fargo, ND
If you want to put in a switch, put it here, in the blue wire. (red circle) Make certain you get the correct blue wire, the one that goes to the over load, not the other heat relay. This will kill both heating coils.
heat strip.jpg
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,071
Location
Northern Virginia
How is your heat pump system breakered?

The ones I am familiar with have (3) 2-pole breakers - one for the heat pack (your "toaster"), one for the air handler, and one for the outdoor unit.

If yours is breakered this way, why not just turn the breaker for the heat pack off?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,411
Location
Richmond, VA
Isn't there a setting in the control/thermostat?
There may be something buried in the settings, but at least on my thermostats (April aire) my only front screen options are heat (which enables both the heat pump and backup, controlled by the setpoint) and emergency heat (which forces the backup to run). I don't have an easy way to disable the backup source.

Maybe other thermostats are different though.
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,966
Location
Peace Valley,mo
If your low voltage board has a humidifier terminal should drop out 24 vac when unit goes into defrost. 24 vac relay with N.O. contact in series with aux heat wire.
 
OP
W

WaterBoyz

Well-known member
Joined
Nov 16, 2015
Messages
368
Location
Northern VA
Isn't there a setting in the control/thermostat?
The Ecobee has AUX settings but mainly for when to engage it. Today, the outside temp was at 3º, so the Ecobee turned on the AUX to heat, knowing the heat pump can't do it. If I did the switch-out today, the system would run and run since the Ecobee would not know the AUX was disabled.
 
OP
W

WaterBoyz

Well-known member
Joined
Nov 16, 2015
Messages
368
Location
Northern VA
If you want to put in a switch, put it here, in the blue wire. (red circle) Make certain you get the correct blue wire, the one that goes to the over load, not the other heat relay. This will kill both heating coils.
heat strip.jpg
That is where I was going to go, but wanted additional input since I'm not an official HVAC ....just an overqualified tinkerer.
 
OP
W

WaterBoyz

Well-known member
Joined
Nov 16, 2015
Messages
368
Location
Northern VA
How is your heat pump system breakered?

The ones I am familiar with have (3) 2-pole breakers - one for the heat pack (your "toaster"), one for the air handler, and one for the outdoor unit.

If yours is breakered this way, why not just turn the breaker for the heat pack off?
I do have two circuit breakers. One feeds just the single heat pack. The other feeds the double heat pack and the air handler. If I'm reading the drawing correctly.
 
OP
W

WaterBoyz

Well-known member
Joined
Nov 16, 2015
Messages
368
Location
Northern VA
There may be something buried in the settings, but at least on my thermostats (April aire) my only front screen options are heat (which enables both the heat pump and backup, controlled by the setpoint) and emergency heat (which forces the backup to run). I don't have an easy way to disable the backup source.

Maybe other thermostats are different though.
My Ecobee has an AUX setting, but mainly when to turn it on. Not really a setting to turn completely off.
 
OP
W

WaterBoyz

Well-known member
Joined
Nov 16, 2015
Messages
368
Location
Northern VA
If your low voltage board has a humidifier terminal should drop out 24 vac when unit goes into defrost. 24 vac relay with N.O. contact in series with aux heat wire.
I glanced at the drawing for the air handler and did not see a humidifier. I'll have to look better later. Great idea.
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,411
Location
Richmond, VA
Adjust the setting tona ridic value so it never comes on?
Aux heat gets triggered by a couple things, one is outdoor temp, another is how far off the interior set point is from actual interior temp. So if I click my tstat up by 10 degrees, it will trigger the Aux regardless of the outdoor temp.

There should be settings for all this, but it may mean making a bunch of changes and it may mean there is something that can't be fully overridden
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,390
Location
VT
Aux heat gets triggered by a couple things, one is outdoor temp, another is how far off the interior set point is from actual interior temp. So if I click my tstat up by 10 degrees, it will trigger the Aux regardless of the outdoor temp.

There should be settings for all this, but it may mean making a bunch of changes and it may mean there is something that can't be fully overridden

I did a bit of reading and see the aux heat comes on automatically during defrost too, regardless of settings.

Sounds like he has to physically disconnect it to prevent it from kicking on and tripping the genny
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,106
Location
SE MI
If you want to put in a switch, put it here, in the blue wire. (red circle) Make certain you get the correct blue wire, the one that goes to the over load, not the other heat relay. This will kill both heating coils.
heat strip.jpg
Correct answer !
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,622
Location
Fargo, ND
That is where I was going to go, but wanted additional input since I'm not an official HVAC ....just an overqualified tinkerer.
Plus, it is low voltage, 24 volts at that point so just a cheap toggle switch will do.

I can understand what you are trying to do, but some of the sugestions don't get it! I can see not changing the settings i nthe thermostat and just walking over and flipping the switch. Changing the settings means you have to enter the code to the set up menu, change some setting and then change it back and hope you don't accidentally screw something else up.

I would go with the switch!

I have a two stage furnace. The furnace is a bit over sized and will heat the house fine on low fire until -30F. (I tested it once, unintentionally, when the out door temps dropped a bit lower than -30F and the furnace didn't keep up!) My thermostat has a control board mounted near the furnace and I unscrew the second stage wire so it never runs unless I hook the wire back up. I should put a switch on the second stage wire, but I have run second stage one time in ten years, so it isn't much of an issue!
 
OP
W

WaterBoyz

Well-known member
Joined
Nov 16, 2015
Messages
368
Location
Northern VA
I did a bit of reading and see the aux heat comes on automatically during defrost too, regardless of settings.

Sounds like he has to physically disconnect it to prevent it from kicking on and tripping the genny
The AUX is triggered by the outside unit when it goes into defrost mode. The Ecobee is not involved. That is why I'm going to put a switch on the blue wire route. It is only a concern during the winter AND while on the generator.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,390
Location
VT
The AUX is triggered by the outside unit when it goes into defrost mode. The Ecobee is not involved. That is why I'm going to put a switch on the blue wire route. It is only a concern during the winter AND while on the generator.
Yes, that's what I was getting at...
 
OP
W

WaterBoyz

Well-known member
Joined
Nov 16, 2015
Messages
368
Location
Northern VA
Plus, it is low voltage, 24 volts at that point so just a cheap toggle switch will do.

I can understand what you are trying to do, but some of the sugestions don't get it! I can see not changing the settings i nthe thermostat and just walking over and flipping the switch. Changing the settings means you have to enter the code to the set up menu, change some setting and then change it back and hope you don't accidentally screw something else up.

I would go with the switch!

I have a two stage furnace. The furnace is a bit over sized and will heat the house fine on low fire until -30F. (I tested it once, unintentionally, when the out door temps dropped a bit lower than -30F and the furnace didn't keep up!) My thermostat has a control board mounted near the furnace and I unscrew the second stage wire so it never runs unless I hook the wire back up. I should put a switch on the second stage wire, but I have run second stage one time in ten years, so it isn't much of an issue!
Yeah, I understand the programming route. But since the only concern is during the winter AND while on the generator. So, the switch is my plan.

Thanks...........
 