Code requires the equipment to be installed according to the manufacturere's instructions. The requirement for a fused disconnect is dictated by the manufacturer. If the equipment data plate states "use a maximum overcurrent device rated at ** amps" you do not need a fused disconnect. If it says "maximum fuse size ** amps" there needs to be fuses somewhere in the circuit between the breaker and the unit and a fused disconnect is the easiest way to accomplish it. If it says something like "maximum breaker or fuse size ** amps" you have the option of going with breakers or fuses.
Tommy
Tommy,
Great point and it's been so long since I encountered an appliance that was fuse only on the name plate I did not even consider that in my reply. The fact that the unit is a Fujitsu and primarily marketed in Asia (where fuses are more commonly used still) it's possible that it does say "Max Fuse Size".
I just looked that model up on their web site and it seems to indicate Max Fuse size (although one document said 20 amps and another said 30 amps).
I would like to see a picture of the units physical name plate to see how it's actually worded on it.
If it says "Max Fuse Size" only then Tommy is right, it would need a fused disconnect despite what I said in my earlier post.
OP, you still need the proper circuit breaker protecting this circuit and the proper wire size as well.