I want to send my plan to inspector before doing actual work. Reading NEC I found only that 250v disconnect has to be below 6'7", laterally 36" and no farther then 50' and visible. Any thing else? Like distance to obstacles ( fence and equipment itself in my case). Some one said 36" between compressor and disconnect. But I can't find this in the code. Thank you.
1699214315266.png
 
To avoid these ads, REGISTER NOW!

briceandy4

Member
Joined
Oct 22, 2023
Messages
8
The 36” that someone told you was probably for working clearances. In your case this shouldn’t be an issue. Just place the disconnect in a readily accessible location and you should be good.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,000
Location
Central Iowa
You need a clear width of 30" in front of the disconnect. That 30" wide space has to be at least 36" deep. Nobody is going to put a disconnect at 6'7", but if you thought about putting it on the ceiling, don't. The disconnect has to be within sight, which by definition is within 50' and unobstructed from view. As long as you don't put the disconnect behind the compressor and a short person can reach it, you're ok.

Most of this will be found in 110, I think .26 but I'm not going to get off the couch to go check.
 
Last edited:
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,071
Location
Modesto, CA
why are you putting UF-b in EMT? that wont be fun and its a waste of money. just get individual conductors.

is this an air conditioning compressor or air compressor?
 
OP
S

strobes

Active member
Joined
Oct 27, 2023
Messages
43
I have UF-b in hand. And it's 4'-5' run with one bend. If difficult just little bit of dish soap will make a difference I think.
 