Disconnect wiring ?

AP514

Well-known member
Joined
Jan 23, 2014
Messages
768
Location
Pearland, Tx
Hi all...

I set this disconnect up for my 240 v compressor. Im going to have a inter cooler w/fan set up at some point in the near future( note to self get off your lazy **** and finish it up).

My question is should I have a Ground Block installed in the disconnect or is the Wire NUT ok ?
 

Attachments

  • Cutoff.jpg
    Cutoff.jpg
    135.9 KB · Views: 119
To avoid these ads, REGISTER NOW!

m.b.0331

Well-known member
Joined
Nov 22, 2013
Messages
70
Location
Maryland
Install a ground lug in the disconnect. If the box itself becomes energized, the ground lug will provide a good path to ground. Right now, the box is not grounded.
 
OP
A

AP514

Well-known member
Joined
Jan 23, 2014
Messages
768
Location
Pearland, Tx
Well, the garage is steel frame/grounded...and the box is screwed into the Frame..

But good point..........
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,767
If you still have the bonding screw for the neutral bond it & use it for grounding.
 

m.b.0331

Well-known member
Joined
Nov 22, 2013
Messages
70
Location
Maryland
Well, the garage is steel frame/grounded...and the box is screwed into the Frame..

But good point..........

I was going to add something about that. Yeah, if the box did become energized, the steel frame might provide a good path to ground, but you can't really rely on that to keep you safe. The ground lug provides a sure fire way, and a proper way, to ground your equipment.
 
OP
A

AP514

Well-known member
Joined
Jan 23, 2014
Messages
768
Location
Pearland, Tx
Not really sure how the box could get energized but the ground block seems the way to go.....((I guess I could just put another wire (to ground the box) in the wire NUT. Where my solid is connected to the stranded.) I hope ground block is cheap at my local HD.....
 

m.b.0331

Well-known member
Joined
Nov 22, 2013
Messages
70
Location
Maryland
It is unlikely that the box could become hot, but it could happen. Over time, maybe, a lug holding one of your hot wires (line side, of course) could loosen and a wire could pop out and touch the disconnect, energizing it.

All you really need is a ground lug and a piece of green wire (looks like 10AWG). Install the ground lug, strip out some of your wire and put that end in the lug, tightening it down nicely. Strip out the other end and join it to the two wires in the wire nut. Now the box is grounded. We use these ones at work:

http://www.zoro.com/i/G0279657/?utm...uFOb1KDJrDSN-ten5ImmZhejL1CZQaTVMQaAhCX8P8HAQ

If our ground wire just needs to be 12awg, we use premade grounding pigtails.

You can install the lug a number of ways, some are proper and some are hack...A self tapping screw would work but it's kind of hack. A nut and bolt or a screw in a tapped hole could work too. The goal is to make the lug fit tightly to the box.
 

m.b.0331

Well-known member
Joined
Nov 22, 2013
Messages
70
Location
Maryland
the box calls for a GTL1..ground lug

I'm not familiar with a GTL1 and a google search brings up this thread and not much else. The example I posted above is the lug we commonly use for these applications, though. It fits wire sizes 4-14. You should be able to find that type at HD.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,767
When I use a safety switch w/ a solid neutral like the OP's switch & there is no neutral needed or present, I use the bonding screw to bond the enclosure to the neutral bar & use it to land the equipment grounding conductors, I should have elaborated further in my earlier post, it makes things quite simple, rather then chasing down a grounding lug using what is already there.
 
OP
A

AP514

Well-known member
Joined
Jan 23, 2014
Messages
768
Location
Pearland, Tx
Interesting that a 240v load has a neutral.

True, but Im adding a Fan for the intercooler on my compressor..So I needed a Neutral(pulling the 120v from one of the power legs off compressor)
here is the NEW fan got it for $35 on EBAY (plastic capasitor was craked off of the base EZ glue job to repair)
http://www.onlinecomponents.com/ebm-papst-w2e250hj3201.html?p=12104374.

So I wanted to be really safe and put the Neutral on the cut off. (no way no how power is getting to it once the power is cutoff) besides it was an open spot so I used it :p
 
Last edited:

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,767
While it is permitted to switch the neutral as long as they are switched at the same time as the ungrounded (hot) conductors there is no reason to do so in the OP's case. it has a solid neutral & my previous comments can be disregarded.:D

I do it when I need a cheap disco for 120V equipment, so I use a 60A non-fusible pullout A/C disco.
 
OP
A

AP514

Well-known member
Joined
Jan 23, 2014
Messages
768
Location
Pearland, Tx
Ordered the $ 3.50 from HD..wil be here soon..

Also I should have said in my OP that this cut off is going to my compressor. solid to the cutoff and Stranded from there...

Thanks for the input
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
While it is permitted to switch the neutral as long as they are switched at the same time as the ungrounded (hot) conductors there is no reason to do so in the OP's case. it has a solid neutral & my previous comments can be disregarded.:D

I do it when I need a cheap disco for 120V equipment, so I use a 60A non-fusible pullout A/C disco.
:thumbup::thumbup::thumbup::thumbup:
 
OP
A

AP514

Well-known member
Joined
Jan 23, 2014
Messages
768
Location
Pearland, Tx
Well,quick update installed the Ground bar...Cleaned paint off of box where bar sits
 