I use to have access to Daikin University and what you have posted is not what is taught. You reference to 300 psi test Which Daikin recommends 600 psi makes me think this is old info for an R 22 system.Same with the Daiken manual
I’m going to check with one of the techs at work and see what they say. I’ve got some other irons in the fire but I believe I can work on this a little each day. I got the inside unit hung today.
I’m definitely going to need some help fishing the lineset through and will probably wait until my son can help. Hopefully have this wrapped up my the end of next week.
Typical, running my mouth without having the correct info. this is an AC only unit not a heat pump. AC only must run
I give up when I looked up the model the internet said AC only. I wondered why someone would spend that much for AC only.

Profit margin for sure, I often here quotes for $4-6000 or more for a minisplit install.No offense to the HVAC installers out there. But in my opinion mini splits are just through wall units that got split in two and are no sustitute for a central system with proper distribution, filtration and humidity contol. Yet they get pushed hard by HVAC companies because the profit margin, ease of install and low risk of call backs. Not that its the best solution for the customer.
What the install manual for this unit says is; pull a vacuum for 30 minutes, if it holds, fill the system. That’s it, no mention of a pressure test, nitrogen, or a micron gauge.

Well if summer doesn’t get here quickly I’m in no hurry. First day the temps are 84*+, test over, start the unit."That’s it, no mention of a pressure test, nitrogen, or a micron gauge."
As to a pressure test, I can question the need for a high pressure test to a point, though you still need nitrogen purges. As to not using a micron gauge, you could easily miss a slow leak without using one, it also cuts down how long you need to monitor your mechanical pressure gauge for leaks and moisture, all the while of having to consider ambient temperature changes.
"The EPA has defined small appliance as 5# or less of refrigerant,"
Technically the amount of 410a used in many minisplits is under 5lbs but it is a high pressure refrigerant thus type II
"if you work on any system that doesn't qualify as a small appliance or low pressure system....you need type II or universal certification"
Fully agree the EPA's chance of bothering an individual is about zero, if they are going to bother anyone, it a business with deep pockets. I got my universal to buy gas, and maybe I can get a repair part under a warranty.
Aside from that, the entire EPA 608 laws are warped. Example...If you have a very large low pressure system such as a chiller with hundreds of pounds of refrigerant, it is OK to have rupture disks to vent gas (all or nothing); if the EPA is so worried, they would mandate a pressure relief system which it should be. Also I like the percent of gas leakage allowed and time frame large systems get for repairs; basically they can let 100s of pounds of gas leak, god forbid I let an oz of gas release . The 608 cert reminds me of the asbestos regulations, where the government should NOT be making up the regulations.
Metimunchr, thanks for the precharged line info.
Sort of Russian Roulette, 90-95% of the time you will have no problem, but watch a mechanical gauge for only 2 minutes... your pulling the tiger with 1 round in a six shooter. If your system has a (very)slow leak, watching a gauge for 2 minutes, the needle will not move, it might not move in multiple hours, whereas with a micron gauge you will see it immediately; my gauge starts at 25000 microns, so I have 25000 increments, and the meter updates in a fraction of second .
As to the nitrogen purge, as long as your vacuum gets all the moisture, your fine; get all the moisture in 15 minutes, unlikely, be prepare for a longer vacuum time, then with a Nitrogen purges. Are you sure you got all the moisture? a micron gauge is far more accurate than gauges.
No high pressure test, you will probably will be OK, as long as your vacuum test really shows no leak, then again in 1-2 minutes I would say it is absolutely totally IMPOSSIBLE to catch a small leak with mechanical gauges in that time frame. With a tiny leak maybe in 24 hours, than again you will need to be great at compensating for ambient temperature changes.
My point, why have doubts with a high cost item (even with a steep discount, rebates and tax credits). Even if it ends up costing you very little, it is a pain in the *** to replace, and of course it will fail at an inopportune time. At least buy or borrow a micron gauge; check the gauge has no leaks, think that is unlikely.... I bought (2) new Elitech VG-760 Digital micron gauges within a few weeks of each other, both leaked massively, finally got a used Yellow Jacket 69086, no leaks.
That's because the DIY target market doesn't own tools to do the work and/or doesn't want to buy them.
Coils!!! Upright coils look like an oil trap to me, but I am not a HVAC engineer, but am burdened with common sense. I would lay coils flat and above service valves on unit. One bright young fella made a roof/cover above the unit and put the coil in it!My use is in a metal workshop building and while the engineer in me will not like the coiled lines, if I measure carefully I can probably just put the indoor units were ever the end of the line falls.
It is doubtful that a micron gauge is defective out of the box.Follow up;
Even though the Daiken installation manual doesn’t mention a micron gauge, I do want the level of QA it provides. I was looking to buy one/reading reviews and started getting apprehensive hearing so many of them not working right out of the box. I called a local HVAC service company and asked what they’d charge to do it at their convenience. $85 for leak test, vacuum, and start up. That’s a no brainer in my situation. I’m “involved” with an HVAC service company but our area is 70 miles from me, I can’t cover the costs of one of our techs coming out or buy a micron gauge for $85.
On the one hand; I believe it’s probably not as common as the reviews on Amazon would leave one to believe. On the other; seeing a dozen reviews on every gauge I looked at claiming DOA didn’t exactly give me the warm & fuzzies either.It is doubtful that a micron gauge is defective out of the box
IIRC Daikin University and what appears to be the knowledgeable techs on You Tube say to remove the light weight flair nuts and use the heavier ones on the units. Noticeable difference in the bulk and weight of the unit flair nuts.I have always heard to cut off the factory lineset flares, and remake them.

Who?"Now reading the manuals, I think we will be seeing lots of failed DIY installs here."
Agree, it seems we have some members who are proud of how many improper installation procedures they can get away with...beats me considering how expensive minisplits and service calls are.![]()