DIY wiring a 3 phase compressor?

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
The OP's starter looks good to go for a 7.5 HP 1Ø motor, and looks like the control X-former is already set for 230V, the only thing left is the painful part, buy a new motor & new heater coils for the overload relay.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Ok so its a DP- definite purpose, contactor, which most likely means the coil cant be changed.

The coil is 120v based on the control transformer label.

looks like the primary side of the CT is connected to 230v, so you're good there.

what is the rating on the fuses? they may need to be changed.

The contactor is rated for 7.5HP 230v 1Ø, so you're good there.

Can't tell what size wire comes off the overload block but it needs to be 50a rated wire, #8 THWN
 
Last edited:
OP
G

GlennRobinson

Member
Joined
Jun 23, 2020
Messages
20
Location
Western PA
Prepare for information overload ....

attachment.php


attachment.php


attachment.php


attachment.php


attachment.php


attachment.php
 

Attachments

  • IMG_1248.jpg
    IMG_1248.jpg
    61.7 KB · Views: 109
  • IMG_1246.jpg
    IMG_1246.jpg
    99.7 KB · Views: 110
  • IMG_1249.jpg
    IMG_1249.jpg
    88.4 KB · Views: 110
  • IMG_1250.jpg
    IMG_1250.jpg
    150 KB · Views: 110
  • IMG_1251.jpg
    IMG_1251.jpg
    164.7 KB · Views: 109
  • IMG_1252.jpg
    IMG_1252.jpg
    160.1 KB · Views: 110

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
the heaters you have are E7- 21.9-24.4a. too small for a 7.5HP 1Ø motor, which would have an FLA of around 35a.

Doesnt look like that heater series goes above 33a.
 
OP
G

GlennRobinson

Member
Joined
Jun 23, 2020
Messages
20
Location
Western PA
Thought I had an idea of how much I didn't know. Guess I was wrong.

So does this mean I am back to looking a phase converter or VFD?

Glenn
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
Why does the photo with the MAIN breaker have 4 Breakers tied to one handle?

Because it's a factory assembly, it is actually a 2 pole breaker, ITE was the first company to build them that way in the mid 1970's, Cutler-Hammer, GE, & I think SQ D copied the idea.
 
OP
G

GlennRobinson

Member
Joined
Jun 23, 2020
Messages
20
Location
Western PA
Update - While cleaning up the compressor, I went to empty any condensation in the tank and was quite surprised at the volume. I drained 30-40 GALLONS of rusty water. Based on this finding, I am returning the compressor to the seller. He has agreed to a full refund.

A big thanks to everyone for the education. I will be limiting my shopping to single phase compressors.

Glenn
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Update - While cleaning up the compressor, I went to empty any condensation in the tank and was quite surprised at the volume. I drained 30-40 GALLONS of rusty water. Based on this finding, I am returning the compressor to the seller. He has agreed to a full refund.

A big thanks to everyone for the education. I will be limiting my shopping to single phase compressors.

Glenn

:shocking: :wtf:

wow thats a lot
 

DeeKay

Well-known member
Joined
Nov 25, 2020
Messages
448
Location
Colorado
Update - While cleaning up the compressor, I went to empty any condensation in the tank and was quite surprised at the volume. I drained 30-40 GALLONS of rusty water. Based on this finding, I am returning the compressor to the seller. He has agreed to a full refund.

A big thanks to everyone for the education. I will be limiting my shopping to single phase compressors.

Glenn

Wow, that's a lot of water. Good call on returning it. Good luck on the compressor search!
 