Hello all, I disassembled this GE 3hp Triclad motor cleaned everything, replaced the capacitors and bearings. Got to thinking setting it back up on the compressor (well my son did) man that motor is heavy. Is this motor control equipment even necessary with a capacitor start motor? I get a humming noise from it every once an a while when it starts and I have to shut it off and restart it again.
Any advice would be appreciated,
 

Attachments

  • 20231024_175658.jpg
    20231024_175658.jpg
    809.2 KB · Views: 43
  • motor pictures.jpg
    motor pictures.jpg
    643.3 KB · Views: 42
To avoid these ads, REGISTER NOW!

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
14,009
Location
West central Indiana
Most pumptrol pressure switches are current limited, many at 1.5 to 2 hp on single phase, hence the need for them to actuate a magnetic starter instead of passing the motor current through to the pumptrol directly. If it hums and doesn't start, you likely have a problem with the motor or control. Possibly one of the capacitors is bad(new doen't mean its good) or one of the contacts on the magnetic starter is pitted/burnt and not making correct contact every time.

The unloader could be malfunctioning as well
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
10,941
Location
Rhode Island
If the humming is coming from the motor starter (and the motor otherwise starts normally), it's probably just the contactor is old/worn. They can sometimes hum when they get old.
 

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,097
Location
AZ
Fire summed up everything that could be an issue nicely. I’d look at the contacts in the starter first. If they’re burned and pitted either dress them or replace.
 
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,710
Location
NW Iowa
The box is a motor starter. It has nothing to do with it being a capacitor start motor or not.

The starter provides overload protection as well as a much heavier set of contacts than is in the pressure switch.

The humming is nothing to worry about. Lots of starters do it if they get a little rust in the iron core. Some even do it when brand new.
 

Steve_P

Well-known member
Joined
Sep 15, 2010
Messages
5,182
I would inspect the contacts. I'm sure they will at least need to be dressed, if not replaced, unless someone did it recently.

On my home air conditioner, once it was ~15 years old, I was going thru a capacitor on the compressor about every two years. And the ends of the wiring showed evidence of high current- insulation looked like hell near the connectors at the capacitor. So I was clipping the ends of the wires and replacing connectors every few years- and running out of wire. I talked to the HVAC guy and he said it was normal as the compressor ages, etc. At some point I noticed the contacts looked like ****, they were rusty, so I removed them, blasted them, and copper plated them. That ended my issues and I haven't replaced a capacitor since. Or maybe one 10 years. And I haven't changed a connector since.
 
OP
J

jamurr65

Member
Joined
Oct 28, 2018
Messages
18
Location
central square ny
Thanks to all, that explains it all quit well. I got to looking at the starter and wondered how the heck I even figured out how to hook it all up.
Must have done an awful lot of research. probably most came from this forum.
Thanks again
 