Do I need a cap on this conduit?

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,480
Location
Richmond, VA
Hey all,

Building a screened porch and wiring some outlets in the 6 x 6 box around the outside perimeter. You can see the conduit coming up with a wire that will go to horizontal outlets. Do I need to put any kind of bushing or anything on that or can I just run the wire to the outlet straight out of the conduit?
There will be a top board completely sealing it in.
 

Attachments

  • IMG_6051.jpeg
    IMG_6051.jpeg
    957.7 KB · Views: 116
  • image.jpg
    image.jpg
    687.6 KB · Views: 116
To avoid these ads, REGISTER NOW!

Chuckster in NJ

Well-known member
Joined
Jan 26, 2010
Messages
2,318
Location
Hunterdon County NJ
Hey all,

Building a screened porch and wiring some outlets in the 6 x 6 box around the outside perimeter. You can see the conduit coming up with a wire that will go to horizontal outlets. Do I need to put any kind of bushing or anything on that or can I just run the wire to the outlet straight out of the conduit?
There will be a top board completely sealing it in.
You can put a PVC connector with a bushing on it and seal the top of the bushing with duct seal to keep bugs out.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,652
Location
Long Island
I would cap that pipe with a female thread adapter, then screw into that a UF squeeze connector.
shopping
 

JohnX14

Well-known member
Joined
Jun 2, 2014
Messages
603
Location
Boston 'burbs
You can do what Chuckster said. It's better than leaving it as-is, but it'll be fine if you leave it as-is.

Edit: you can do what rlitman suggested. I wouldn't bother.
 

BreeStephany

ALLIANCE MEMBER
Joined
May 19, 2012
Messages
854
Location
Oregon
While conduit sleeves in the case of the sleeve for your UF are not required to be accessible, I would personally run conduit continous between 2 boxes / pull points and pull proper conductors between those pull boxes.

How long is the sleeve that you are pulling the UF through?

As for whether a cap is required, I would put a terminal adapter with a nonmetallic bushing on it at minimum, but if the conduit goes to another junction point or the sleeve exceeds 8' in length, I would not use UF and would have a continous conduit between pull points.

Just my thoughts.
 
To avoid these ads, REGISTER NOW!
OP
J

jpcjguy

Well-known member
Joined
Jan 6, 2014
Messages
1,480
Location
Richmond, VA
Other end goes into the crawlspace. Once final connections are done I will seal the conduit end but I am not anticipating anything because the the end in the picture will be completely seald
 