Do I need a remote disconnect box??

Tim Fitzgerald

Well-known member
Joined
Dec 1, 2013
Messages
60
Location
Anacoco, La
tankless water heater 30 foot run from main service panel

Draw 13,000 watts

60 amp breaker wired with 6 ga wire

What does code say, do I need an additional disconnect and what is the language that mandates this...?

does it matter if I run romex or strand

also I have seen some hooked up where they installed a plug set up instead of hard wire...from what Ive seen this would negate having a separate disconnect

If I were to choose this route, what would be the specs for outlet and plug end that I should be looking for on packaging...

Hopefully I have supplied enough info to get a credible answer...thanks in advance for your help
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Can you see the panel from the heater? As I recall residential doesn't call for one on a water heater. I wouldn't want any between the breaker and the unit if I could help it.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,207
Location
SE MI
Can you see the panel from the heater? As I recall residential doesn't call for one on a water heater. I wouldn't want any between the breaker and the unit if I could help it.

I think that is the key.

Running stranded in conduit is much easier. Southwire says max ampacity on #6 Romex is 55A.
 
Last edited:
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You need to hardwire it. A 60 amp plug and socket will cost you a couple of hunded dollars. Romex in #6 is gonig have stranded conductors and not solid.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Is there a wiring guide in the owners manual? I know if I was the mfg would be looking to get this just in an approved installation with a number 6 cable for residence.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
One thing to consider as a rule of thumb. If they wanted a plug on it they would have one. They provide a point of service connection, like other water heaters, fixed equipment like bathroom fan. Reason they use extra connection in AC is that its remote away from the incoming connection to the equipment,,, poor explanation,,,, but air comp is fixed etc. and doesn't come with fac pak cord.
 