Do I need "Tamper Proof" Receptacles?

OP
S

sideways

Well-known member
Joined
Aug 21, 2010
Messages
77
Location
North Eastern Maryland
I plan on biting the bullet and replacing my recepts with TP. But, can I use my existing 12-3 wiring if I change the wiring from its current configuration of alternated circuits. How can I used the existing runs?
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,775
I plan on biting the bullet and replacing my recepts with TP. But, can I use my existing 12-3 wiring if I change the wiring from its current configuration of alternated circuits. How can I used the existing runs?

You break off the tab on the hot side.
 

5lima30

Well-known member
Joined
Nov 11, 2010
Messages
2,442
Location
Mountains of Western NC
I had to have the tamper proof outlets to pass my final inspection in Western NC. As soon as I got my CO I swapped them out for conventional outlets. I still have GFCI outlets on the exterior. YMMV.
 
To avoid these ads, REGISTER NOW!

bww_mnm

Well-known member
Joined
Dec 30, 2010
Messages
673
Location
Chicago area
a quick call to your inspector or city/count office would answer your initial question on need for TR outlets in your city/county.
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
You can share the neutral up to the *first* GFCI outlet. From that point on, you need separate neutrals for both sets of outlets. You should only require two GFCIs, one for each branch. You'd only be saving wire to the first GFCI however, which may not be a significant savings.
 