So getting some wiring done and wondering if I'm overly concerned about voltage drop in my outlets. I ran some in slab conduit but not enough. So the longest run about 120' one way, it will have 2 or 3 outlets and then 2 outlets for garage door openers. The outlets will see occasional shop vac, or battery charger, the vac pulls about 12amps (peak?), the openers 1 amp each. So running 12 gauge NM-B on 20 amp breaker was the plan.
Looking at a Voltage Drop chart 12amp load, 120v, 12 AWG one way run is 78'. If I go to 10AWG length is 124' for 12amp , and 99' for 15amp.
I doubt those things will be used at the same time, but just wondering what would be correct thing to do.