Do I need to ground Metal Junction Boxes?

Bolson32

Well-known member
Joined
Dec 6, 2016
Messages
541
Location
Lake Elmo, MN
Title, mostly.

I recently ran a sub and rewired my garage using PVC conduit with metal Junction boxes...I know I know....it's not EMT but I didn't have the time or frankly the want to deal with EMT. 5 year garage at most.

Now to the meat and potatoes of the question...should these junction boxes be tied to the ground with a pigtail? I'm not sure if that's practice where people run romex to metal or not. Theoretically if you have a loose wire couldn't the junction box become hot and a potential shock hazard?
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
Metal boxes where splices and devices exist need to be grounded.

Metal boxes need to be bonded to the grounding conductor. If it was a metallic conduit, then the above quote applies.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Metal boxes need to be bonded to the grounding conductor. If it was a metallic conduit, then the above quote applies.

When I said grounded, I meant the equipment ground wire of the circuit needs to be connected to the box. So how is bonding the box with the EGC not grounding the box? :headscrat
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
When I said grounded, I meant the equipment ground wire of the circuit needs to be connected to the box. So how is bonding the box with the EGC not grounding the box? :headscrat

You were saying where splices or devices exist, a metal box / enclosure used with a non-metallic raceway needs to grounded PERIOD.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,995
Location
Modesto, CA
Yeah, a metal box that is not connected via metallic raceway, is isolated and can become accidently energized creating a shock potential.

Whther there are splices or devices in the box does not change the bonding requirement.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Yeah, a metal box that is not connected via metallic raceway, is isolated and can become accidently energized creating a shock potential.

Whther there are splices or devices in the box does not change the bonding requirement.

Thanks for saying it the way you did because Norcal's first response had me confused about my answer. I understand all metal boxes need bonding. I was precisely responding to the OP's comment about possible loose connections in a junction box. I didn't mean to imply that metal boxes with splices or devices are the only boxes that needed bonding. I know what I'm talking about, sometimes I just don't type it out in a clear answer.
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,725
Location
SE Michigan
If you use the 4" square metal boxes, some styles have a dimple in the stamping which is already tapped 10-32. Which is the perfect size for the "preassembled ground pigtail". I like the stranded ones which I can only seem to find at Menards.

Here's an example.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,888
Guessing it needs a ground screw?

Sent from my SM-G935V using Tapatalk

NEC requires two complete threads of the screw in the box. Metal boxes are, at minimum and almost universally, 1/16 of an inch thick, which means a 32 tpi screw. Most metal boxes have a tapped 10-32 hole for grounding. On boxes intended for surface mounting, it's raised, on other boxes, it's not. You do not need to use a special screw, just one that's properly made. You may, if you wish, do so. (They're cheap.)
 

prostreetamx

Well-known member
Joined
Dec 19, 2016
Messages
222
Location
Las Vegas
Some inspectors actually want the screw also to be painted green so a normal screw will fit but still not be correct. Grounding pigtails already have a green screw.
 

tab2

Well-known member
Joined
Apr 9, 2009
Messages
381
Location
Boston
I use these:

https://www.amazon.com/dp/B00CDVJA0A/?tag=atomicindus08-20

Can buy local home depot or lowes as well. I know not stranded but does come with the green screw already attached and ready to go....if you have a lot of boxes to do saves a little time. Especially with my fat fingers the wire holds the screw in place lol

These are what I see on site (and permanently borrow from the electricians when I need some at home).
 