Does a Double-Tapped meter become a Distribution Point?

John in OH

Well-known member
Joined
Jun 2, 2007
Messages
2,444
Location
SE Ohio & Eastern Virginia
So here is a question ....

The plan for my new detached garage is a new 150amp main panel in the garage with disconnect and sub-breakers. Source will be a second connection to the LOAD side of the existing house meter (double-tap) that is fed by a 400amp service from the power company.

Originally, I thought I'd need only 3 conductors (2 hot + 1 neutral) from the meter to the new panel with grounding rods at the new panel ... essentially a duplicate setup to the feed into the house.

But now I'm wondering if this double-tap arrangement creates a "distribution point" arrangement where a 4 conductor (2 hot + 1 neutral + 1 full size ground) feed is required by NEC from the meter to the new panel?

Any insights or thoughts??
 
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Since you would be tapping directly off the meter base with no service disconnect ahead of these wires, you would run a 3 wire feed to your building. This building would have a service rated disconnect and all your grounding would happen here. After this point everything must be 4 wire.

Run this setup by your inspector first. I know most around here would probably want a disconnect right beside the meter before running unfused conductor over to another building. If that happens, then you would need 4 wire.
 