Does anyone know the correct way to wire a 650R outlet?

BooRadley

Well-known member
Joined
Jun 20, 2010
Messages
47
This is for a welder. 250/50. Crooked handyman wired for me a circuit that isn't code, and an outlet that is incompatible with my welder. Circuit isn't code because he used 10/2 when code says to use 6/3. But since I will be using welder for thin materials only, and infrequently, 10/2 will do. I'll never pull more than 20 amps max with this welder, and usually less, so, I won't bother changing the wire out. But I do need to change the outlet to a nema 650.

What I need to know which wire goes where? Instructions on box are useless, and nothing on the outlet is marked. I have wired other outlets before, but never a 650R, so I need to check to make sure what i have in my head is the right thing to do.

P.S. Handyman won't honor his 'guarantee', so that is not an option. Bad man, and I've no more money to spend on this matter, so I have to do it myself. :(
 
Last edited:
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
note that a 6-50 is a 2 pole 3 wire receptacle, if you were wiring it with #6 romex, you would use 6/2 not 6/3
 
OP
B

BooRadley

Well-known member
Joined
Jun 20, 2010
Messages
47
So, it doesn't matter which hot wire goes to which flat blade? If not, fabulous! Thanks very much.
 
OP
B

BooRadley

Well-known member
Joined
Jun 20, 2010
Messages
47
This welder draws 41 Amps when run on the highest setting. As I understand it, 10/2 is not to be used with a 50 Amp breaker, and is not supposed to take more than a 30 Amp load. According to NEC. Is that right? I could be wrong.
 
Last edited:

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
This welder draws 41 Amps when run on the highest setting. As I understand it, 10/2 is not to be used with a 50 Amp breaker, and is not supposed to take more than a 30 Amp load. According to NEC. Is that right? I could be wrong.

theres another chart for welders only that takes duty cycle into account and allows smaller wire (although I dont like it esp. in residential situations) your 10/2 is fine, it would be a good idea to label the receptacle 'welder use only'
 
To avoid these ads, REGISTER NOW!

JimDon

Well-known member
Joined
Jan 23, 2007
Messages
603
which welder? yes NEC OKs smaller wire for welder circuit only because of overall duty cycle. If you're running a buzz box or a Miller 210 or something comparable , you're gonna be just fine with that 10-2w/Gr. Even with a decent sized Tig, your hands are gonna get hot way before the wire will. way way way too many people who weld at home think a 10% duty cycle is going to be surpassed regularly. WRONG! With most projects, you'll be re-positiong, moving around , changing sticks, etc. to even get close. I run the piss out of my Miller buzz box all the time and never ever get those 10-2 cables warm.
Cheers,
JimDon
 
OP
B

BooRadley

Well-known member
Joined
Jun 20, 2010
Messages
47
Hi Jim. Here she be:
http://www.northerntool.com/shop/tools/product_200381950_200381950

164609_lg.jpg
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
Be careful that there is not a minimum AWG size for that outlet. Wiring with a smaller (your 12 AWG) may create problems if it is designed for a minimum of #8.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
i looked at a leviton 6-50 i have and it has a wire range of #10-#4 CU/AL
 

W-Cummins

Well-known member
Joined
Jan 9, 2006
Messages
1,642
Location
Iowa
theres another chart for welders only that takes duty cycle into account and allows smaller wire (although I dont like it esp. in residential situations) your 10/2 is fine, it would be a good idea to label the receptacle 'welder use only'

I don't like it either in a non commercial install. If I were the inspector I would NOT pass it. I also feel the same way about the reduced (sec 430) motor wire requirements. Unless it was a non-plug ( hardwired ) I would fail them too. There is just too great of a chance the next home owner will plug in some thing else in. Even if it's marked, some one paints the wall, and the next guy plugs in a range and cooks the 10 gauge wire!

William...
 