Does Building code or electrical code determine hole placement in studs?

TimberMan

Well-known member
Joined
Apr 6, 2024
Messages
184
I failed my rough in electrical inspection because one hole for Romax was allegedly drilled within 5/8 of an inch of the stud edge. I’m gonna measure it because I don’t think it’s that close but if it is, does “building code” govern this dimension or does the NEC govern this dimension?

Thanks
 
To avoid these ads, REGISTER NOW!

jd_1138

Well-known member
Joined
May 8, 2013
Messages
17,066
Location
NE Ohio
Seems it'd be an electrical code issue. Don't want the wires too close to the drywall or other wall material due to fire risk. I don't think it would weaken the stud too much in terms of structural rigidity.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,293
Location
VT
pic of the issue?

What size stud?

Will the inspector allow you to put a nail plate over it?
 

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,328
Location
Alexandria, VA
IIRC, NEC states that the hole for the wire must 1 1/4" back from the edge of the stud, and a standard 2x4 stud is about 3 1/2" deep. If its less than that depth you must protect it with a nailing plate.

I usually recess the nailing plate just enough so it is flat with the stud face, to avoid bulges when you install the drywall.
 
OP
T

TimberMan

Well-known member
Joined
Apr 6, 2024
Messages
184
Yeah that's a pretty obvious fail. 2x4 can be tough, 2x6 leaves you miles of space. Drill more towards center

Did you have the plates in it during inspection?
Yes, plates were in ahead of inspection as shown. I can’t find anything in the NEC that says what is pictured is a fail since I have protected the wire with the metal plates.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,028
Location
Coronado, CA
In addition to having to protect the cables from being damaged by nails and screws driven into them; the stud has to be protected by not being weakened by drilling holes too big or too close together.

In my opinion both the Structural and Electrical Codes need to be addressed.
 
OP
T

TimberMan

Well-known member
Joined
Apr 6, 2024
Messages
184
In addition to having to protect the cables from being damaged by nails and screws driven into them; the stud has to be protected by not being weakened by drilling holes too big or too close together.
Agreed, but is that part of building code or NEC?
 
OP
T

TimberMan

Well-known member
Joined
Apr 6, 2024
Messages
184
Both address the situation, but from different perspectives; again the answer is "It Depends".
Reason I’m focused on this detail is that the structure is a barn and categorize as “agricultural” therefore, I do not need to meet building code. If I can show that this hole location issue is for building code then he’s gonna have to pass me because that’s outside of his jurisdiction for this building.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,293
Location
VT
Reason I’m focused on this detail is that the structure is a barn and categorize as “agricultural” therefore, I do not need to meet building code. If I can show that this hole location issue is for building code then he’s gonna have to pass me because that’s outside of his jurisdiction for this building.
If the electrical inspector failed your electrical inspection, then this is part of the NEC.

Can you ask him for clarification, as you have plates? How hard is fixing those 3 holes?
 

Hank11

Well-known member
Joined
Aug 19, 2019
Messages
1,157
Location
Tennessee
If you need an electrical inspection you have to pass it.

If not real difficult, re-pull those two wires into new holes.

Otherwise, drill new holes in the middle of the stud, shift the wires back and plug the old holes with wood and glue and/or sister a piece of 2x6 to support the stud.
 

pcmeiners

Well-known member
Joined
Aug 13, 2009
Messages
7,948
Location
In the only town in Pennsylvania, Bloomsburg.
Reason I’m focused on this detail is that the structure is a barn and categorize as “agricultural” therefore, I do not need to meet building code. If I can show that this hole location issue is for building code then he’s gonna have to pass me because that’s outside of his jurisdiction for this building.
Novel idea...ask the inspector why he failed the inspection and for the fix.

It does not pay to inform the inspector that it not in his jurisdiction unless you want to be be more aggravated and need lots more work.
 
Last edited:

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,833
Location
Southern Oregon
2017 NEC 300.4 (A)

(1) Bored Holes. In both exposed and concealed locations, where a cable- or raceway-type wiring method is installed through bored holes in joists, rafters, or wood members, holes shall be bored so that the edge of the hole is not less than 32 mm (1-1 ∕4 in.) from the nearest edge of the wood member. Where this distance cannot be maintained, the cable or race‐ way shall be protected from penetration by screws or nails by a steel plate(s) or bushing(s), at least 1.6 mm (1 ∕16 in.) thick, and of appropriate length and width installed to cover the area of the wiring. Exception No. 1: Steel plates shall not be required to protect rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, or elec‐ trical metallic tubing.
Exception No. 2: A listed and marked steel plate less than 1.6 mm ( 1 ∕16 in.) thick that provides equal or better protection against nail or screw penetration shall be permitted.
 
OP
T

TimberMan

Well-known member
Joined
Apr 6, 2024
Messages
184
Novel idea...ask the inspector why he failed the inspection.

It does not pay to inform the inspector it not in his jurisdiction unless you want to be be more aggravated and need lots more work.
I have and am waiting on his feedback but in the meantime I want to understand if I need to change anything at all.
 
To avoid these ads, REGISTER NOW!

carcruse

Well-known member
Joined
Apr 7, 2007
Messages
218
Location
SE Michigan
2017 NEC 300.4 (A)

(1) Bored Holes. In both exposed and concealed locations, where a cable- or raceway-type wiring method is installed through bored holes in joists, rafters, or wood members, holes shall be bored so that the edge of the hole is not less than 32 mm (1-1 ∕4 in.) from the nearest edge of the wood member. Where this distance cannot be maintained, the cable or race‐ way shall be protected from penetration by screws or nails by a steel plate(s) or bushing(s), at least 1.6 mm (1 ∕16 in.) thick, and of appropriate length and width installed to cover the area of the wiring. Exception No. 1: Steel plates shall not be required to protect rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, or elec‐ trical metallic tubing.
Exception No. 2: A listed and marked steel plate less than 1.6 mm ( 1 ∕16 in.) thick that provides equal or better protection against nail or screw penetration shall be permitted.
Based upon this: "Where this distance cannot be maintained", I'd say inspector is correct, it is part of his jurisdiction and in your case steel plates will not solve your problem. You could have maintained the required distance.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,028
Location
NJ
Stud on the left only has 2 plates. Need a 3rd to cover lowest cable to comply with NEC. Yes you can get another nail plate on or replace the singles with triples.

Have him tell you which code section you failed for.
 
Last edited:

carcruse

Well-known member
Joined
Apr 7, 2007
Messages
218
Location
SE Michigan
Also, most Building Codes state no holes in wall studs shall be closer than 5/8" to the outer edge of the stud. Hard to tell from the pictures but you might just barely be ok there.
 
OP
T

TimberMan

Well-known member
Joined
Apr 6, 2024
Messages
184
Also, most Building Codes state no holes in wall studs shall be closer than 5/8" to the outer edge of the stud. Hard to tell from the pictures but you might just barely be ok there.
That’s my hope since I don’t need to meet building code; only electric code.
 

Tracs

Well-known member
Joined
Feb 1, 2015
Messages
568
Location
Manitoba, Canada
That’s my hope since I don’t need to meet building code; only electric code.
You are not wrong wanting to show that your work is correct and wanting clarification, but arguing to the inspector that the hole is 11/16" and not 5/8" from the face might not be the best course of action.
 
OP
T

TimberMan

Well-known member
Joined
Apr 6, 2024
Messages
184
You are not wrong wanting to show that your work is correct and wanting clarification, but arguing to the inspector that the hole is 11/16" and not 5/8" from the face might not be the best course of action.
Technically….”no less than 5/8” means that 5/8” is a pass since 5/8” is not less than 5/8”.
 

whateg01

Well-known member
Joined
Mar 13, 2006
Messages
11,405
Location
doo dah, kansas, usa
Novel idea...ask the inspector why he failed the inspection and for the fix.

It does not pay to inform the inspector that it not in his jurisdiction unless you want to be be more aggravated and need lots more work.
OP says because hope is less than 5/8" from edge of stud. Looks like a fail in the pic as well.

If it doesn't need to meet any code, why is there an inspection?
 
OP
T

TimberMan

Well-known member
Joined
Apr 6, 2024
Messages
184
OP says because hope is less than 5/8" from edge of stud. Looks like a fail in the pic as well.

If it doesn't need to meet any code, why is there an inspection?
There are only inspections for trades: plumbing, electrical and mechanical… building code does not apply
 

cmandp

Well-known member
Joined
Dec 22, 2011
Messages
1,284
Location
New Jersey
Hopefully he can clarify but to my understanding if they are protected by nail plates as you have, its a pass per the NEC.

I'd be polite but firm about it and reference the applicable code @yatg quoted above.
 

kngelv

Well-known member
Joined
May 25, 2011
Messages
2,230
Location
Detroit, MI
It's pretty clear from the NEC that all of his holes are too close to the stud edge. The OP could have installed the holes per the code but chose not to do so. The nail plates are irrelevant according to the first part because he could have drilled them in the right place. The plates don't give you a pass on the first part. It's very clear the OP did not follow the code which is why he failed the inspection.

James
 

paulsomlo

Well-known member
Joined
Jul 16, 2013
Messages
3,904
Location
Northern Colorado
You could have eyeballed the center of that stud, drilled 1 hole and put everything through it and you'd never have to argue with the inspector.

Why did you drill so close to outside?
Exactly - once the inspector saw the holes that close to the edge of a 2x6, it immediately sent up a red flag.
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,483
Location
Northern Virginia
Do the plans call for 2x6 for structural reasons or just insulation depth?

Our houses are designed at 2x4 but we use 2x6 for insulation.
 