2017 NEC 300.4 (A)
(1) Bored Holes. In both exposed and concealed locations, where a cable- or raceway-type wiring method is installed through bored holes in joists, rafters, or wood members, holes shall be bored so that the edge of the hole is not less than 32 mm (1-1 ∕4 in.) from the nearest edge of the wood member. Where this distance cannot be maintained, the cable or race‐ way shall be protected from penetration by screws or nails by a steel plate(s) or bushing(s), at least 1.6 mm (1 ∕16 in.) thick, and of appropriate length and width installed to cover the area of the wiring. Exception No. 1: Steel plates shall not be required to protect rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, or elec‐ trical metallic tubing.
Exception No. 2: A listed and marked steel plate less than 1.6 mm ( 1 ∕16 in.) thick that provides equal or better protection against nail or screw penetration shall be permitted.