Does BX require a j-box at the entry point?

esvee

Well-known member
Joined
Dec 28, 2014
Messages
171
Location
Portland, OR
I'm running surface outlets in my garage and all power will be coming in from the ceiling. If I transition from romex to BX in a junction box in the attic - can the BX just pass through a hole in the drywall at the wall joint (garage ceiling) or does there need to be a surface mounted junction box on the ceiling?
 
To avoid these ads, REGISTER NOW!

bamawildcat

Well-known member
Joined
Jul 12, 2014
Messages
148
It can pass through a hole. Needs to be secured with 12" of the box and every 4.5 feet.
 

Jkcolo22

Well-known member
Joined
Nov 28, 2018
Messages
74
Location
Castle Rock, CO
Somebody may correct me, but I’m pretty sure that all connections must be accessible. Meaning that junction box can’t be hidden in the attic. It should have an exposed face plate. With BX, you should be using metal boxes, and you could use a faceplate with a knockout and run the BX out of that. Kill two birds with one stone.


Sent from my iPhone using Tapatalk
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,750
Be aware that AC, "BX" & MC, cable have the same requirements for protection from physical damage as NM cable "Romex®".
 

Jkcolo22

Well-known member
Joined
Nov 28, 2018
Messages
74
Location
Castle Rock, CO
Be aware that AC, "BX" & MC, cable have the same requirements for protection from physical damage as NM cable "Romex[emoji2400]".


But isn’t it true that AC BX and MC can be installed in “exposed” locations, whereas NM can be installed in enclosed locations?


Sent from my iPhone using Tapatalk
 

bamawildcat

Well-known member
Joined
Jul 12, 2014
Messages
148
Somebody may correct me, but I’m pretty sure that all connections must be accessible. Meaning that junction box can’t be hidden in the attic. It should have an exposed face plate. With BX, you should be using metal boxes, and you could use a faceplate with a knockout and run the BX out of that. Kill two birds with one stone.

As long as he has access to the attic, no issue with putting a box up there. You would be right however, it can't be buried. I would reckon he would have said put it in the ceiling if he was thinking of burying it.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,750
But isn’t it true that AC BX and MC can be installed in “exposed” locations, whereas NM can be installed in enclosed locations?


Sent from my iPhone using Tapatalk

They both have the exact same requirements as NM, if you want exposed use EMT.
 
To avoid these ads, REGISTER NOW!
OP
E

esvee

Well-known member
Joined
Dec 28, 2014
Messages
171
Location
Portland, OR
As long as he has access to the attic, no issue with putting a box up there. You would be right however, it can't be buried. I would reckon he would have said put it in the ceiling if he was thinking of burying it.

Correct - the attic is accessible so no worries there.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,690
Location
NW Iowa
Putting unnecessary boxes in an attic is poor workmanship in my opinion. I agree that it's legal but it's easy to avoid it when running new wiring.
 

Jkcolo22

Well-known member
Joined
Nov 28, 2018
Messages
74
Location
Castle Rock, CO
Putting unnecessary boxes in an attic is poor workmanship in my opinion. I agree that it's legal but it's easy to avoid it when running new wiring.


Yeah it seems to me that if you are running something through the ceiling anyway, then why not just put a J box in the ceiling and run BX or EMT or whatever out of that.


Sent from my iPhone using Tapatalk
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,690
Location
NW Iowa
“Unnecessary” boxes would seem to be an opinion.

Does it need to be there?

Yes it's a little subjective. But it should make you think.

In op's case I think I would sleeve the Romex in emt from the ceiling to the box. Eliminate a splice and box altogether.
 