Does the emt need to be grounded?

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,443
Location
Western North Carolina
Hi,
I am running 2 UF wires, 12/2 & 6/2, from an interior panel to an exterior disconnect.
Doing so I have go through a room where the UF will be in a 2” emt which ends in an exterior wall.
The emt is not connected to any electrical boxes and is only used to hide the UF wire in that one room I have to go through
so my question is does the emt have to be grounded?

Thank you
 
To avoid these ads, REGISTER NOW!

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,949
Location
New England
How would one ground a conduit not ending at a box or device?


Sent from my iPhone using Tapatalk
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,929
Location
NW Iowa
Could use a ground clamp for pipe, a connector on one end with a grounding bushing ( the ends need to be bushed anyway). I'm sure there are other ways also.
 
OP
A

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,443
Location
Western North Carolina
Could use a ground clamp for pipe, a connector on one end with a grounding bushing ( the ends need to be bushed anyway). I'm sure there are other ways also.

The emt ends on the interior side in the room where the main panel is located
around 6’ above from the main panel.
Can I run a ground wire from the main panel to the grounding bushing at the emt?
All the other wires powering the house run up from the panel
and pass the new emt in very close.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
No, because the EMT in your case is a sleeve and there are no splices or wire connections in it. It's not considered a conduit system. You do need bushings on the ends of the EMT
 
OP
A

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,443
Location
Western North Carolina
No, because the EMT in your case is a sleeve and there are no splices or wire connections in it. It's not considered a conduit system. You do need bushings on the ends of the EMT

Just to clarify, no on the grounding and yes on the bushings?




Edit, We are under the NEC 2014 and it will be inspected.
 
Last edited:
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,929
Location
NW Iowa
No, because the EMT in your case is a sleeve and there are no splices or wire connections in it. It's not considered a conduit system. You do need bushings on the ends of the EMT

Looks like you might be right, 250.86 exception 2. I guess it also depends on what we consider a "short section".
 