Hi everybody, background user here, hoping to borrow some of the collective wisdom though.
I'll probably reach out to an electrician at some point, however, I really want to have as good an understanding as a layman can have. Not a stranger to electrical -- my dad and grandfather were both lineman, and I've done a full basement successfully.
Here's my story -- I'm worried I'm getting close to the max on my 200amp service. I live outside Dallas, and here are the specs I've plugged into a couple of load calc spreadsheets: 3200sq ft, 3 small appliance circuits, 1 laundry circuit, 1-5.4kw dryer, 1-5.1kw oven, 1-7.1kw range, 2-4 ton ACs, 2-2.4kw central furnace, dishwasher, 2-refrigerator, 1-1.58kw microwave, 1 range hood, 5 vent fans, 1 disposal, 1 garage door opener, 1 Xmas light circuit, 1 exterior light circuit.
What I'm hoping to add -- 1-50amp RV hookup, 1-60amp hot tub (negotiable), 1-20amp swimming pool filter (above ground, only pulls ~400w), 1-30amp shed/workshop circuit.
Depending on the calculator spreadsheet, it looks like I'm coming out to somewhere around 213 amps if I add 9600w in as an appliance load for the RV hookup and 2 small appliance circuits for the shed and pool (I'm guessing that's not the right way to do it?).
Am I in the ballpark? Or do I need to up my service if I add all that? I've confirmed with the POCO that I can move up to 400amp if I swap the meter, just don't want to go through all that if it's overkill.
What do you think?
I'll probably reach out to an electrician at some point, however, I really want to have as good an understanding as a layman can have. Not a stranger to electrical -- my dad and grandfather were both lineman, and I've done a full basement successfully.
Here's my story -- I'm worried I'm getting close to the max on my 200amp service. I live outside Dallas, and here are the specs I've plugged into a couple of load calc spreadsheets: 3200sq ft, 3 small appliance circuits, 1 laundry circuit, 1-5.4kw dryer, 1-5.1kw oven, 1-7.1kw range, 2-4 ton ACs, 2-2.4kw central furnace, dishwasher, 2-refrigerator, 1-1.58kw microwave, 1 range hood, 5 vent fans, 1 disposal, 1 garage door opener, 1 Xmas light circuit, 1 exterior light circuit.
What I'm hoping to add -- 1-50amp RV hookup, 1-60amp hot tub (negotiable), 1-20amp swimming pool filter (above ground, only pulls ~400w), 1-30amp shed/workshop circuit.
Depending on the calculator spreadsheet, it looks like I'm coming out to somewhere around 213 amps if I add 9600w in as an appliance load for the RV hookup and 2 small appliance circuits for the shed and pool (I'm guessing that's not the right way to do it?).
Am I in the ballpark? Or do I need to up my service if I add all that? I've confirmed with the POCO that I can move up to 400amp if I swap the meter, just don't want to go through all that if it's overkill.
What do you think?