So I'm wiring 3ph outlets in the new shop. Its a 1" trunk line going around the perimeter of the attic with a bunch of 3/4 drops teed into it that drop down to the floor. One common circuit right now feeding all outlets, they all go hot at the same time.
Shop is 25 x 40 so for the very last outlet, it goes thru roughly 100 more feet of conduit after the first outlet.
But I was thinking it would be easy to cut in another tee at this point to make a continuous loop in the trunk line and then I could "double feed" the loop from both ends to reduce voltage drop. That would put the middle outlet roughly 50 feet from the first one, no matter which direction of travel is considered around the trunk line.
The mechanical analogy would be a shop air system where it would be desirable to feed a loop from both ends to reduce starvation of flow.
Seems logical to me although maybe not traditional. I do recall a 1600A x 480vac welding bus being fed from both ends via tie-breaker disconnects just in case of problems but I can't recall if the tie breakers were ever both "connected" at the same time.
For my case, the extra work involved is minimal at this point. Wanted to see about violations or other functional problems with the idea. All the phases are carefully identified
don't want to "cross the streams"
you know....
Shop is 25 x 40 so for the very last outlet, it goes thru roughly 100 more feet of conduit after the first outlet.
But I was thinking it would be easy to cut in another tee at this point to make a continuous loop in the trunk line and then I could "double feed" the loop from both ends to reduce voltage drop. That would put the middle outlet roughly 50 feet from the first one, no matter which direction of travel is considered around the trunk line.
The mechanical analogy would be a shop air system where it would be desirable to feed a loop from both ends to reduce starvation of flow.
Seems logical to me although maybe not traditional. I do recall a 1600A x 480vac welding bus being fed from both ends via tie-breaker disconnects just in case of problems but I can't recall if the tie breakers were ever both "connected" at the same time.
For my case, the extra work involved is minimal at this point. Wanted to see about violations or other functional problems with the idea. All the phases are carefully identified