Yes i know that's a sprinkler pipe, just mocking up.

I have LB pointing UP towards a sub panel (bottom entry, exterior panel)


Is it ok to drill a couple small holes on the bottom of the LB?
 

Attachments

  • IMG_1615.JPG
    IMG_1615.JPG
    64.6 KB · Views: 97
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,319
Location
NJ
Technically not ok wrt the listing, but frequently done. One hole, 1/16 - 3/32" is plenty. Maybe even duct seal into the horizontal conduit.
 
OP
P

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
On a related note, would you drill a hole on the bottom of back to back EMT run?

not saying I would, do you or know some people who does?
 
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,930
Location
NW Iowa
On a related note, would you drill a hole on the bottom of back to back EMT run?

not saying I would, do you or know some people who does?

I never have, but I have debated doing it before. Most of the time I end up with a coupling so it isn't a problem. I have seen conduit split open from water freezing inside and seen it rust out at low points so it is a concern.
 
Last edited:

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,536
Location
Minneapolis
Another option for conduit systems is to install a condensate drain fitting. Crouse-Hinds makes them, I assume the other manufacturers make them as well.


http://www.cooperindustries.com/con...d_drains/cd_series_ordinarylocationdrain.html


cch_f_cd_220.jpg
 