If the inspector says the work is acceptable, the homeowner did his/her part, hired a licensed professional, paid for a permit, the work was inspected and passed, so what else is the homeowner expected to do?
Nothing. Many times in life ignorance is bliss.
But if you are the kind of person who is on this forum be aware that if somebody says "we got a permit and it was inspected, so it meets code" it may indeed not meet code.
Every inspector is tasked with inspecting to the governing code. Sometimes that's the NEC, sometimes it's the IBC, or a PE stamped drawing, or a local spec that is stricter than a national code.
In this case there are very valid reasons to have the ground rod deep into the earth... and not just under the surface... and if the inspector says differently, tell him you are going to modify the drawings to meet his specifications and want him to sign and date it... you'll see him change his mind real quick.
"A driven ground rod must be buried at least 8 ft. in the ground. With an 8 ft. ground rod, the connection to the grounding electrode conductor must be made flush with the ground or below ground. If bedrock is hit when driving the rod, it may be installed at a 45 degree angle. When driving the rod at a 45 degree angle, if bedrock still prevents the rod from being driven, the ground rod may be buried in a trench which is at least 30 inches deep."