Hi All,

I've lurked for a while trying to pick up tips here and there to make sure I'll be happy with what I build.

I'm at the point where I plan on enclosing my carport and have a question about my clothes dryer vent.

Currently the vent exits the side of the house where the carport/garage is. Obviously, I dont want the vent to go into the soon to be enclosed garage increaing temperature, humidity and lint. How do I extend the vent 20 feet?

Thanks in advance.
 
To avoid these ads, REGISTER NOW!

Wardster

Well-known member
Joined
Mar 28, 2008
Messages
372
Location
Kingston, Ohio
I used 3" PVC to vent the dryers in my house, so that is an option. Just add onto it and run out of the carport.

-Wardster
 

rsanter

Well-known member
Joined
Dec 22, 2007
Messages
18,505
Location
visalia ca
if you have a crawl space under the house I would redirect the vent to another location outside of the garage

bob
 

Lou's Garage

Well-known member
Joined
Feb 12, 2008
Messages
581
Location
Anderson, SC
Extending it is possible. Use the solid tubing that's available for dryer venting. From experience, keep it accessible as with that much of a "run" you'll need to open it up to clean it out every year or so.

Lou
 

Jaguar Fan

Well-known member
Joined
Mar 13, 2008
Messages
5,507
Location
Park City for Ski Season; Las Vegas for Poker Seas
Extending it is possible. Use the solid tubing that's available for dryer venting. From experience, keep it accessible as with that much of a "run" you'll need to open it up to clean it out every year or so.

Lou

agreed... every now and then you'll read about a house fire that somehow started in a dryer vent clogged with flammable lint...
 

kbs2244

Well-known member
Joined
Nov 11, 2006
Messages
14,065
The local chimney sweep added "dryer vent cleaning" to the side of his truck.
He works every day now.
Make any elbows where it turns removable so you can open it up for cleaning.
 

Red'n'WhiteRebel

Well-known member
Joined
Feb 22, 2008
Messages
261
Location
Ontario, Canada
Lots of good points already. Don't use flex for sure, don't use screws(foilback tape works great to hold joints tight). Check the dryer's manual for the max pipe length, if it's a gas dryer make sure the termination hood has no plastic parts, HD/ Lowes carries all metal hoods.
 
To avoid these ads, REGISTER NOW!
OP
N

NBN

Well-known member
Joined
Jun 6, 2008
Messages
190
Location
SE Tejas
Guys,

Each of you have been helpful. I was concerned about the potential lint clog and possibility of running the vent so long. I'll just have to make sure the line is cleaned periodically.
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,114
Location
Northern Virginia
Rule of thumb for dryers is 25 foot max, each 90 degree fitting is worth 5 equivalent feet. Use metal pipe, no screws, and tape as suggested above. Can't remember, but its either 4 inch or 5 inch metal duct pipe. Also, use a flapper type discharge wall cap rather than one with a bird screen on it. The bird screen catches too much lint.
 

ebarber

New member
Joined
May 26, 2008
Messages
3
They say not to use PVC or plastic because of the static charge. It will collect lint on the inside and clog quickly. Use metal.
 

Kevin54

MEMBER EMERITUS
Joined
Jan 12, 2005
Messages
29,341
Location
Urbana, Ohio
About 10 years ago when we sided a buds house, he had to extend his dryer vent. He used a rubber coupling to fasten the drop to the straight run and ran a small rope thru the vent tube. When it came time to clean it out, he would tie a large rag and another rope to the rag. One would be in the crawlspace and one outside. A few times of pulling the rope back and forth had the vent as clean as new. He did this on a regular basis, once in the spring and once right before it got real cold out. Never had a problem.
 

randydupree

Well-known member
Joined
Jun 3, 2006
Messages
235
Location
archer fl
the problem with a long vent pipe is the dryer runs longer,it will not dry as well,meaning longer run times.
at least thats what happened to me.
i moved my washer/dryer from my old house to a new house i had built and the dryer didnt dry for squat,a 20' dryer vent pipe was the reason.
i cut a hole in the garage wall and ran a short pipe into the garage and all was well.
a fan would be a must on a 20' run.
Randy
 

MPContractor

New member
Joined
Jun 9, 2008
Messages
1
There are dryer bootster fans available if you need to extend over the recommended length. check out this link:

http://www.fantech.net/dryer_boosting.htm

Depending on how long the run has to be, you may be able to use long turn elbows. They are more airflow efficient and don't require a reduction in run length for each turn. I found it online at www.dryer-ell.com and use them instead of booster fans which can be expensive.
 

6768rogues

Banned
Joined
Nov 28, 2007
Messages
4,524
Location
Western NY
Larry is right on with his statement about typical 25 foot maximum length and an elbow being equivalent to 5 feet. Size is usually 4 inch and you should use rigid aluminum non corrugated duct made for a dryer. Aluminum is noncombustible and will not rust. Moisture is more of a problem with a longer run, so slightly pitch the pipe to the outside and use aluminum. A booster fan can be used, but they require frequent service because of lint, and if they fail they are an obstruction to airflow.
 