Just need advice on what size wire I would need to get 100 amps to a metal building 100
Feet from my house that has a newer 200 amp box installed?
 
To avoid these ads, REGISTER NOW!

Glenn M.

Well-known member
Joined
Aug 8, 2012
Messages
3,186
Location
VA/ SWFL
Welcome to the GJ from VA!

Please ask this question in the Lighting and Electrical forum where the traffic and available expertise will amaze you.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,256
Location
Modesto, CA
#2 Al MHF(mobile home feeder) protected with 90a breaker! CU conductors will blow a hole in your wallet but if u prefer CU then 3 #3 CU wires with 1 #8 CU wire for the EGC protected by a 100a breaker! It doesnt matter that the panel is rated for more than the feeder breaker.

Will this be a one man shop and if so what equipment will be used?
 

matt151617

Well-known member
Joined
Dec 17, 2011
Messages
488
Location
New Jersey
You'll also need to install 2 ground rods, at least 6 feet apart, connected to the panel with #6 copper. And the most important thing- the neutral can't be bonded to the ground in the subpanel.

Are you in the US or Canada? There's a lot more information we need (see post above about equipment).
 