Dual condensate pumps-plumbing?

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
Need some help plumbing condensate lines for Furnace and on demand water heater.

Furnace used to dump into a garden hose snaked across basement. I added a neutralizer and pump, which has a small check valve, clear tubing in a loop and then a barb fitting into a piece of 1" PVC that daylights over in the utility sink.

On demand heater is on the opposite wall of utility room, no good way to gravity drain to the existing pump at the furnace. Was going to add a 2nd pump, but how do I tie this in?

Can I just wye into the existing PVC, add an upstream check on each pump and call it good?

Do I even need check valves, aside from right at the pump?

What if I wanted to tie these into the main sanitary line? I didn't do this initially as it was a trainwreck (mix of PVC, fernco and rubber hose) that has since been re-done.
 
To avoid these ads, REGISTER NOW!

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,990
Location
Northern Virginia
I would keep the pump systems separate so failure of one can't take the other out.

Regarding dumping to the sanitary, it will depend on what your local Code allows. Counties near me are mixed. Most counties have us plumb the mechanical room floor drain to the sump crock and the condensate lines then dump to the floor drain. Other odd county requires that the floor drain be connected to the sanitary system which then receives condensate discharge.
 
OP
P

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
I would keep the pump systems separate so failure of one can't take the other out.

Run a separate line to the sink?

I suppose I could, but not sure how 2 pumps into the 1" drain would take each other out. Or are you referring to my comment about #2 dumping into #1?

I installed that water heater and embarrassingly long time ago, it drains into a 5 gallon bucket. Guess what I recently forgot to empty...

Regarding dumping to the sanitary, it will depend on what your local Code allows. Counties near me are mixed. Most counties have us plumb the mechanical room floor drain to the sump crock and the condensate lines then dump to the floor drain. Other odd county requires that the floor drain be connected to the sanitary system which then receives condensate discharge.

Thinking about this after I typed the OP, it's not worth my time to tie back into the sanitary. This drain is run nice and compact the where if I ever finish the basement it would be 95% hidden. I'll leave that as is.
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,990
Location
Northern Virginia
Run a separate line to the sink?

I suppose I could, but not sure how 2 pumps into the 1" drain would take each other out. Or are you referring to my comment about #2 dumping into #1?

I installed that water heater and embarrassingly long time ago, it drains into a 5 gallon bucket. Guess what I recently forgot to empty...



Thinking about this after I typed the OP, it's not worth my time to tie back into the sanitary. This drain is run nice and compact the where if I ever finish the basement it would be 95% hidden. I'll leave that as is.
If you have a 1" gravity drain, then you could discharge the individual pumps to this common drain. I would be inclined to install a concentric PVC reducer to act as a funnel where the discharge hoses connect.

1728823307049.png
 
OP
P

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
You don't want a direct connection into the sewer. There needs to be a trap and the condensate line drains into that.
Thanks, but that was never a question, and I nixed the idea of tying to the sanitary.
 
Last edited:

djbmw

Well-known member
Joined
Jun 20, 2013
Messages
1,205
Location
Ottawa, Ontario, Canada
Your pumps are supppsed to be mounted as high up as possible to assist the pumps via gravity, as well as to prevent backflow in the event of a pump or check valve failure.

Second, if you mount two competing pumps on a single line then yes, I would personally install check valves on each line, prior to the "T" to prevent back pressure impacting the pumps.

Do you HAVE to tie them together, or can you just run individual lines to the drain?
 
To avoid these ads, REGISTER NOW!
OP
P

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
Your pumps are supppsed to be mounted as high up as possible to assist the pumps via gravity, as well as to prevent backflow in the event of a pump or check valve failure.

Second, if you mount two competing pumps on a single line then yes, I would personally install check valves on each line, prior to the "T" to prevent back pressure impacting the pumps.

Do you HAVE to tie them together, or can you just run individual lines to the drain?

1 pump is pretty much on the floor, as that's where the drain out of the furnace is. IIRC it's rated for like 12' of head, so no issues there.

I could run a separate drain, but I'd rather not run another 30' of PVC
 

djbmw

Well-known member
Joined
Jun 20, 2013
Messages
1,205
Location
Ottawa, Ontario, Canada
1 pump is pretty much on the floor, as that's where the drain out of the furnace is. IIRC it's rated for like 12' of head, so no issues there.

I could run a separate drain, but I'd rather not run another 30' of PVC
A 30' length of pvc hose is cheaper than two check valves and a T connection in my neck of the woods... but both solutions will work.
 
OP
P

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
The area where the pumps need to go,so we can get an idea what you have to work with.
Well one is already installed and has a hose/pipe run up the side of the furnace.

The other would be a picture of an on demand heater and PEX attached to a wall.

I can take a pic later but not really sure how that helps.

Just trying to figure out the proper way to route 2 1/2 hoses into a single 1" PVC like that daylights in a sink.
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
Well one is already installed and has a hose/pipe run up the side of the furnace.

The other would be a picture of an on demand heater and PEX attached to a wall.

I can take a pic later but not really sure how that helps.

Just trying to figure out the proper way to route 2 1/2 hoses into a single 1" PVC like that daylights in a sink.
After more than 40 years in the trades,30 of them as a contractor I've learned to never give estimates over the phone.
Same holds true for plumbing advice,it's a lot easier to figure things out with a couple of pictures to help visualize what you have to work with. Hahaha
 

welder4956

Well-known member
Joined
Apr 8, 2010
Messages
3,103
Location
Birmingham, AL USA
Yes, a check valve on the discharge of each condensate pump is all you need to tie both into a common drain line. You could add a manual shutoff valve on each one in case you need to isolate the pump to repair or replace, but not absolutely necessary.
 