Duct sizing for room

derekeh

Well-known member
Joined
Sep 6, 2013
Messages
63
I'm partitioning part of my garage to make some rooms and I'd like to know what size flex duct i should go with. The bedroom im concerned about is 16 x 12 and will have 1 window. It currently has 7 inch duct feeding one vent. Should I up it to 8 or 9 inch? By the charts I'm seeing the existing 7 will be too small, but I'd like some opinions before I get in the attic to change it. Thanks.
 
To avoid these ads, REGISTER NOW!

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,622
Location
Fargo, ND
I always figure 1 CFM per sqft. A run of 7" flex is around 100 CFM, maybe a bit more depending on the length of the run. I would think about a second 7" run. Plus two smaller runs are easier to fit up registers.
 
OP
D

derekeh

Well-known member
Joined
Sep 6, 2013
Messages
63
I always figure 1 CFM per sqft. A run of 7" flex is around 100 CFM, maybe a bit more depending on the length of the run. I would think about a second 7" run. Plus two smaller runs are easier to fit up registers.
I considered that, but the existing register is in the middle of the room. Going any farther to the back of the room is a near impossible task due to only inches of attic space. That leaves me with the choice of having 2 registers in the middle of the room spaced evenly across the 12ft width, or have the one in the middle and another just a few feet from it towards the front of the the room. Decisions decisions :\
 
OP
D

derekeh

Well-known member
Joined
Sep 6, 2013
Messages
63
On a room that size, I would like to see an 8" split into 2 6" feeding 2 registers.
I know it's probably not ideal, but would having both registers in the middle of the 16 ft be ok? I think.the current one is 3ft off the wall in the 12ft.
Also the main duct goes overhead here. I could just tap into it instead of splitting the 8inch duct.
 
To avoid these ads, REGISTER NOW!

PWC Repair

Well-known member
Joined
Dec 27, 2012
Messages
3,172
Location
Arkansas
I know it's probably not ideal, but would having both registers in the middle of the 16 ft be ok? I think.the current one is 3ft off the wall in the 12ft.
Also the main duct goes overhead here. I could just tap into it instead of splitting the 8inch duct.
Think about flow through the room. If you have ONE central return air then ideally you want supply coming in at the farthest edges of a room. It blows in.....acroos the room.....through the doorway......and heads towards the return. One register on a 12ft wall will take care of that whole wall. If there is another wall with a window, or on the North side of the house, I would probably place the second one in that area.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,622
Location
Fargo, ND
I considered that, but the existing register is in the middle of the room. Going any farther to the back of the room is a near impossible task due to only inches of attic space. That leaves me with the choice of having 2 registers in the middle of the room spaced evenly across the 12ft width, or have the one in the middle and another just a few feet from it towards the front of the the room. Decisions decisions :\
Then one 8" run with a 6x10 register.
 

Dagny

Well-known member
Joined
Jul 25, 2014
Messages
2,984
Location
Northern Wi.
use metal 10 footer insulate it with a boot on it then slide it into the narrow area near the window.
 