I've been a long-time lurker and have always been in awe of the knowledge base on the site that I haven't felt like I had much to contribute. That being said, I have a question about HVAC Ducting.

We recently purchased a home with an old ductboard system in the attic.

The ducting has been patched and still had some splits that I've temporarily repaired but there are still some leaks around the vents and I think the fiberglass is deteriorating etc...

What I would like to do is replace the ductboard with metal round duct of equivalent size. Are there any pitfalls to replacing the original ductboard with metal by doing the appropriate conversion and installed in the same layout and as the original?
 
To avoid these ads, REGISTER NOW!

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,810
Location
SE Michigan
So when you put ducting into the "cold side" of the attic (thinking winter) then it loses a bunch of heat. In summer, flowing AC it can condense on the exterior and introduce water drips in a place you don't want it.

There's insulated round duct, or if you go with rectangle duct it can be "wrapped" in 1" EPS foam insulation (with the silvery skin both sides). I did the latter in my shop build.

The round metal is going to be hard to wrap with anything.

Also look at Carlisle HardCast Foil Grip tape. Very good at sealing both the ductwork and the insulation for air leaks.

Menards has a whole online catalog of metal ductwork. A lot of it is special order to the store, but its the most comprehensive catalog I've yet seen for a non-pro.
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,435
Location
N CA
I would consider the metal in whatever configuration a substantial upgrade. If the duct board is deteriorating it is blowing fiberglass particles into the living space. Not good. Do the research, sizing and insulation well and you will be happy with the system. Also, do not assume that the original is correct. As long as you are doing this go at it with a clean sheet on the sizing.
 

readhead

Well-known member
Joined
Dec 8, 2012
Messages
6,207
Location
Durango, Co.
Replacing the duct board with similar sized round duct will improve static pressure and may quiet it down some. As mentioned above check the sizing. This may be an opportunity to improve delivery. Consider dampers in the branch runs to help balance. Depending on the size of the house you may want to zone the system. There are plenty of insulation wrap options for round duct. On a very basic level this is DIY but it may be worthwhile to have some HVAC contractors look at it.
 

OccupantRJ

Well-known member
Joined
May 15, 2009
Messages
11,534
Location
Eastern North Carolina
I did my shop system in the attic with round duct. It is relatively easy to work with. I wrapped it in 4 foot wide duct insulation after totally sealing it with brush on duct sealer.

After taping the insulation joints with UL listed metallic tape, I then went an extra step and lightly banded the duct insulation every foot with soft vinyl banding. I did not want to have to worry about insulation coming loose at a later time as I am not getting any younger. I have used the round metal duct on two systems so far and would recommend it.

I did my homework on airflow and sizing, and the system seems to flow nicely.
 

Attachments

  • 993AE600-E434-49F6-ACE7-ECC8D4C9680D.jpeg
    993AE600-E434-49F6-ACE7-ECC8D4C9680D.jpeg
    76.5 KB · Views: 76
Last edited:

metlmunchr

Well-known member
Joined
Sep 10, 2011
Messages
1,285
You can buy sleeve type fiberglass insulation for all common sizes of round duct. It eliminates 90% or more of the required taping. Makes the duct installation a bit slower since you work the sleeve onto the pipe as you go, but its a hell of a lot simpler than getting a good wrap job on previously installed pipe.
 

Ohmthis

Well-known member
Joined
Jan 20, 2013
Messages
3,045
Location
Outside of Louisville KY
Any idea how old the ducting is? Duct board has a finite life span, as I think you are finding out. Metal is in my opinion sooo much better that what you have. Correctly designing the new duct layout is extremely important to the ability of the system to work properly. My advice is to have the duct system professionally designed. There are online services for this if you find it difficult to find someone locally. It would **** to go through the time and investment of putting a new system in, to have it be not quite right. Good luck and post up any questions you might have.
 
To avoid these ads, REGISTER NOW!

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,322
Location
Dutzow Missouri
Duct work in an attic is a very bad idea. All duct work leaks. The only question is how much, weather it is 5% or 40% it is pointless waste.

You sound like a good candidate for mini split system.

Walta
 

PWC Repair

Well-known member
Joined
Dec 27, 2012
Messages
3,223
Location
Arkansas
Is the original system a sort of chase that runs directly over the hallway with a dump into each room basically right by the doorways?
 

danski0224

Well-known member
Joined
Jan 29, 2005
Messages
13,854
Location
Near Naperville, IL
Snap lock round is cheaper than square. Spiral tube is expensive.

CT

Straight 10 foot lengths of spiral is cheap, pricing is not much more than 26 ga snap lock round.

They get you on the accessories like elbows, couplings and so forth.

That said, when the parts and labor are considered for an installed and sealed job, the rubber gasketed spiral and fittings is faster than going back and sealing the non-gasketed stuff.
 

nsula_country

Well-known member
Joined
May 23, 2013
Messages
1,534
Location
Northwestern Louisiana
Straight 10 foot lengths of spiral is cheap, pricing is not much more than 26 ga snap lock round.

They get you on the accessories like elbows, couplings and so forth.

That said, when the parts and labor are considered for an installed and sealed job, the rubber gasketed spiral and fittings is faster than going back and sealing the non-gasketed stuff.

Good to know. I will have to look into the rubber gasket fittings. I have only seen the hard fittings that require sealing.