Ductless mini-split - how many evaporators?

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
I have Mitsubishi Mr. Slim ductless mini-split systems in my house for air conditioning. I have an outside condenser right outside my garage with two indoor evaporators connected to it inside. Can I add a third evaporator in my garage? How many evaporators can be connected to a single condenser? I tried searching online and couldn't find an answer.
 
To avoid these ads, REGISTER NOW!

chinboys

Well-known member
Joined
Jun 20, 2011
Messages
434
certain manufacturers have a central freon control manifold and electronics controller supplement that you put into a central area and then run up to 4 different zones from.
The thing is you cannot exceed the total cooling tonnage or power requirements on this set up by running more zones (splits) than what the system was designed for.
I have a 54K BTU LG condenser that is feeding 3/8 inch liquid to a 4 zone remote box to which I have 4 -9K BTU ceiling units hanging off of returning 3/4 vapor back to the condenser. and I have 3 12K BTU wall units directly plumb into the same condenser manifold with. I will use the upstairs units when I am done for the day but the downstairs wall units will be on while I am wake.

hope this helps
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,217
Location
SE MI
Just look at the outside unit where the existing pipes connect. Modern ones usually have 4-5 max.
 

Git

Well-known member
Joined
May 18, 2008
Messages
6,894
Location
S Cal
What is the model number

My outdoor 24k unit can handle up to 3 connections with 2 currently in use.

You will probably have to pull a panel off to see the ports or maybe we can look it up by model number
 

Muzzy

Well-known member
Joined
Jun 20, 2015
Messages
335
Location
Northeast PA
I had one installed last fall, and it has three sets of ports.

As mentioned, the way I understand it is that you need to consider the size of the indoor units before adding additional load.

i.e. I have two 18K heads on a 30K condenser, meaning that I'm exceeding the capacity of the condenser with the two I already have despite the piping being capable of supporting a third unit.
 

Git

Well-known member
Joined
May 18, 2008
Messages
6,894
Location
S Cal
I think it is pretty common to exceed the total capacity - it all depends on how you think you are going to use it. I have a 24k outside unit with an 18k in the garage and another 6 in my adjacent 'office'. I could easily add a 3rd unit and still be in good shape
 
To avoid these ads, REGISTER NOW!

justinjoyal

Well-known member
Joined
Apr 30, 2015
Messages
888
Location
Quebec
Manufucturer's have their own guidelines when it comed to matching different inside units to multi-zone mini-split systems.

It is indeed common to exceed the rated BTU capacity of the compressor (again following the guidelines).
 
OP
E

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
I snapped a picture of the condenser nameplate
 

Attachments

  • 20160216_174542.jpg
    20160216_174542.jpg
    141.6 KB · Views: 27
OP
E

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
Thanks guys. I looked up the model number of the evaporators I have, and it looks like they're 9,000 BTUs each. So I should have plenty of available BTUs for my 440 sq ft garage.
 