No, it is a tandem breaker. It only contacts one leg in your panel. You can only get (2) 120 volt circuits out of it. You would need a two pole breaker, which contacts both legs
 
Last edited:
OP
D

DavidR8

Well-known member
Joined
Aug 27, 2019
Messages
269
Location
Victoria, BC
Sorry for the double post, not sure why that happened.
I get why you’re saying now. Thanks


Sent from my iPhone using Garage Journal
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,763
So I won’t get 240v if I run a leg from each side?


Sent from my iPhone using Garage Journal

No, as others have already said, there a couple of obsolete makes, Crouse-Hinds, and Challenger, that would allow that to happen, plus can be done in GE panels with GE breakers, but SQ D HOM twin breakers do not allow 240V loads, as it is physically impossible for anything other then 120 volts, BTW those breakers can only be used in a SQ D Homeline panel, as they have not been UL classified to be used in competitive panels.
 
To avoid these ads, REGISTER NOW!

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
No, as others have already said, there a couple of obsolete makes, Crouse-Hinds, and Challenger, that would allow that to happen, plus can be done in GE panels with GE breakers, but SQ D HOM twin breakers do not allow 240V loads, as it is physically impossible for anything other then 120 volts, BTW those breakers can only be used in a SQ D Homeline panel, as they have not been UL classified to be used in competitive panels.

The link shows a QO breaker, will only fit in a QO panel
 

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,828
Location
Southern Oregon
You can put two QO tandems next to each other with a handle tie (QOTHT) for the inner pair. It'll be 240 but not common trip.
 
OP
D

DavidR8

Well-known member
Joined
Aug 27, 2019
Messages
269
Location
Victoria, BC
You can put two QO tandems next to each other with a handle tie (QOTHT) for the inner pair. It'll be 240 but not common trip.


Thanks, that’s what I was thinking about with my original question.
If the resulting 240v are connected to a single device, say a motor and the draw exceeds the 15A capacity would both sides trip?

Sent from my iPhone using Garage Journal
 
Last edited:

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Thanks, that’s what I was thinking about with my original question.
If the resulting 240v are connected to a single device, say a motor and the draw exceeds the 15A capacity would both sides trip?

Sent from my iPhone using Garage Journal

Looks like that would work, thought you meant if you could get 240 v out of that single tandem breaker. Yes both sides will trip. That is what the tie handle is for. A lot of breakers are not internally connected.
 
Last edited:
OP
D

DavidR8

Well-known member
Joined
Aug 27, 2019
Messages
269
Location
Victoria, BC
Looks like that would work, thought you meant if you could get 240 v out of that single tandem breaker. Yes both sides will trip. That is what the tie handle is for. A lot of breakers are not internally connected.


Thanks Terry, in fact that was the thinking behind my original question until it was pointed out that there’s only one connection to the bus.
I didn’t have a breaker handy or I would have figured that out. Eventually.


Sent from my iPhone using Garage Journal
 

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,828
Location
Southern Oregon
Thanks, that’s what I was thinking about with my original question.
If the resulting 240v are connected to a single device, say a motor and the draw exceeds the 15A capacity would both sides trip?

From the QO catalog:
"Order two QOT1515 or QOT2020 circuit breakers and handle tie QOTHT for common switching of center two poles."

The handle tie only gives you a common disconnect vs. common trip. If one breaker trips the handle tie is not guaranteed to pull the other breaker off.

When I replaced my panel several years ago, I used regular size QO115 and QO120 breakers with handle ties for the MWBCs.
 