electical wire for Air Compressor

december45

Well-known member
Joined
Apr 13, 2009
Messages
1,580
went to HD and looked at their 60 gallon Air Compressor, $438.00 where i want to place the compressor is about 100 feet from the electrical panel box, i got a 20 amp receptical and a 20 amp 2 pole breaker, can i use 12/2 wire (romex) for this, tagging the white wire with black tape? thanks for your help

the compressor is 220 vt 15 amp
 
To avoid these ads, REGISTER NOW!

CenTex52Chevy

Active member
Joined
Jun 19, 2008
Messages
38
Location
Coupland TX
Someone more knowledgable than me will chime in soon, but if it was me I would up size the wire to a 10 guage. You may experience some voltage drop due to the lenght of the run, also if you upgrade you compress at a later date you already have the wire in place for a 30 amp service.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
voltage drop calc says you need #10 for 20amps and #12 for 15amps. Since it is a motor load, i would go with #10 myself...
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
The wire needs to be 125% of the FLA of the motor, 12 would suffice with that unit since its 15A. 100 ft is so-so, could be better but if its not constant run deal likely wont make much difference. You can try a 20, if it doesn't trip OK, if it does trip on starts, (usually about half a dozen or so) put a 30 in.
 
To avoid these ads, REGISTER NOW!

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,057
Location
Coronado, CA
1. 12 Guage will work, I would use RED or BLUE tape.
2. 10 Guage would be better, but #1 still applies
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Dammit, my whole post just got deleted!:mad:

To sum it up once again, what you posted is legal. However if it was mine I would use #10 on a 30 amp breaker with a 30 amp receptacle. It's not worth chancing premature motor failure from constant undervoltage at startup using #12. For a few dollars more why take a chance?

Whatever you decide, the receptacle must match the breaker rating.