I have a Goodman A36-20 heater that heats my house, but I have a tap for my garage. I have a Honeywell 7 day programmable thermostat in the hallway. It won't turn off even if I have the thermostat off or even unwired off the wall.
https://goo.io/nJwYmJ
There are two heating element modules, one is 5kW and the other is 15kW. The 15kW unit is made up from three 5kW strings. My first problem was that the middle string cracked a porcelain insulator and although it didn't burn through, every time the sequencer would call that string up, it would trip the breaker. My solution was to remove the jumper wire off the high limit. Then every time that string was called on to start, I wouldn't have any heat, but all I'd have to do is turn the thermostat off, then on and it would sequence to the next element.
Eventually that no longer worked, so I replaced the 15kW module ($70)and everything seemed fine, but it got cold and I had no heat every so often. Not sure if it ever worked right. I called a guy we do HVAC projects with and he said it was likely the sequencer, so $20 later and I'm good to go.
It all worked fine for a couple days, then the breakers started tripping again. What happened was that one of the female connectors that comes directly from the unit breaker was loose and had vibrated off the terminal on the module. This also had a wire jumpered onto it that lead to the 24v transformer. I figured the timer might be bad so I replaced it ($18)and I also replaced the transformer ($12), even thinking that wasn't it. (It wasn't) I also swapped out a high limit switch on that string with one from the old module.
Now I'm thinking it's either the sequencer of the thermostat, but again, if the thermostat is off, the unit still runs.
I'm going to pull the elements out again to give them another inspection but I'm at a loss. What I've spent so far is cheaper than a service call, but all I'm doing is throwing parts at it.
https://goo.io/nJwYmJ
There are two heating element modules, one is 5kW and the other is 15kW. The 15kW unit is made up from three 5kW strings. My first problem was that the middle string cracked a porcelain insulator and although it didn't burn through, every time the sequencer would call that string up, it would trip the breaker. My solution was to remove the jumper wire off the high limit. Then every time that string was called on to start, I wouldn't have any heat, but all I'd have to do is turn the thermostat off, then on and it would sequence to the next element.
Eventually that no longer worked, so I replaced the 15kW module ($70)and everything seemed fine, but it got cold and I had no heat every so often. Not sure if it ever worked right. I called a guy we do HVAC projects with and he said it was likely the sequencer, so $20 later and I'm good to go.
It all worked fine for a couple days, then the breakers started tripping again. What happened was that one of the female connectors that comes directly from the unit breaker was loose and had vibrated off the terminal on the module. This also had a wire jumpered onto it that lead to the 24v transformer. I figured the timer might be bad so I replaced it ($18)and I also replaced the transformer ($12), even thinking that wasn't it. (It wasn't) I also swapped out a high limit switch on that string with one from the old module.
Now I'm thinking it's either the sequencer of the thermostat, but again, if the thermostat is off, the unit still runs.
I'm going to pull the elements out again to give them another inspection but I'm at a loss. What I've spent so far is cheaper than a service call, but all I'm doing is throwing parts at it.