autoist
MEMBER EMERITUS
In the new cathedral ceiling entry to my garage, I've made a "boo-boo". My 3-way light circuit operates in only one way. Lemme explain.
I have a switch at the door from the breezeway connecting the garage to the house and another where you leave the entry/pantry & enter the garage; they are the 3-way circuit. When the switch neatest the breezeway is turned on, the lights work. Then, I can walk to the garage and turn the lights off or on.
Problem is, if the switch at the breezeway is in the 'off' position, and I come into the breezeway/pantry from the garage side, the switch there won't turn the lights on. The switch at the breezeway is controlling the circuit even though power comes to the circuit from the switch nearest the garage door.
If I switch the black & white wires at the switch nearest the breezeway, the lights won't work from either switch. A continuity check from the garage door switch to the breezeway door switch shows that the black wire exiting the garage door switch to the lights ends up as a white wire at the breezeway switch.
I thought I have the circuit hooked up just like all my other 3-ways: power - switch - light - light - switch w/'traveler' connecting both switches.
Both light boxes are in the rafters; I can get to the first light from above without removing shingles because there's another set of rafters 3' right above it; however, I can't get to the 2nd light because the rafters it is in are the actual roof rafters. If that confuses, there's a roofline change right at the 1st light:
This photo shows the change in roofline during construction:
Finished area:
Is it possible to correct the circuit without tearing out my new sheetrock or without ripping the shingles and OSB off the roof at the 2nd light? In other words, can I fix the problem at the 1st light?
I have a switch at the door from the breezeway connecting the garage to the house and another where you leave the entry/pantry & enter the garage; they are the 3-way circuit. When the switch neatest the breezeway is turned on, the lights work. Then, I can walk to the garage and turn the lights off or on.
Problem is, if the switch at the breezeway is in the 'off' position, and I come into the breezeway/pantry from the garage side, the switch there won't turn the lights on. The switch at the breezeway is controlling the circuit even though power comes to the circuit from the switch nearest the garage door.
If I switch the black & white wires at the switch nearest the breezeway, the lights won't work from either switch. A continuity check from the garage door switch to the breezeway door switch shows that the black wire exiting the garage door switch to the lights ends up as a white wire at the breezeway switch.
I thought I have the circuit hooked up just like all my other 3-ways: power - switch - light - light - switch w/'traveler' connecting both switches.
Both light boxes are in the rafters; I can get to the first light from above without removing shingles because there's another set of rafters 3' right above it; however, I can't get to the 2nd light because the rafters it is in are the actual roof rafters. If that confuses, there's a roofline change right at the 1st light:
This photo shows the change in roofline during construction:
Finished area:
Is it possible to correct the circuit without tearing out my new sheetrock or without ripping the shingles and OSB off the roof at the 2nd light? In other words, can I fix the problem at the 1st light?