There is no NEC allowance to use the next smaller size conductor for the motor supply conductors if the calculated amp size is not listed in the tables as is the case for 60C temp for #10 which is 30A, not 35A. Based on needing 35A you will need to use either #8 NM-b at 40A(60C) or #10 THHN at 35A(75C). If the devices in the panel are rated only at 60C then you use #8 at 60C.
I emailed the instructor at electrician math and got this reply
"Howdy. Thanks for your note. You are right to question the article number for
this claim. I went looking in about the 2002 NEC when this material was
generated. No success. You might want to check earlier editions of the NEC. I
would not have included that note if it was not a part of the code at the time
the material was written and typed. That could be 1999 or so. But with limited
time I can only rely on my memory for now. If I find the citation, I'll let you
know.
Anyway, there was a time when this was the approved calculations technique. No
more.
Meantime I have corrected the webpage by deleting that short paragraph.
Thanks for pointing out the error. I depend on my students in the classes I
instruct to do the same. And for sure the branch circuit conductor has to be at
least 125% of the motor FLC from the table for a standard motor. When it comes
to calculating other types of motors with the duty designation, then often there
is some different aspect to incorporate.
Cheers:>) David U. Larson "
So you are correct but do you recall this ever being code compliant in the past as he suggests or is he covering his ***?