Electric to detached Garage

BaltimoreMatt

New member
Joined
Nov 23, 2010
Messages
3
Can anyone help me with determining what electric I need to run to my new garage? Currently there is a single 20AMP circuit coming from a subpanel off of a 150AMP main. The wire looks like 14-3 run in 1" conduit.

The subpanel looks full. I jsut want to have 8 4 bulb flourescents and enough juice to run some power tools and a possibly a compressor and mig welder.

Can I just replace the 20amp breaker with a higher anmp and run 10-3 wire and call it a day?

Thanks
BaltimoreMatt
 
To avoid these ads, REGISTER NOW!

gatchel

Well-known member
Joined
Dec 12, 2009
Messages
672
Location
West of King of Prussia, PA
I would do some searching here. There are loads of topics that will help you. 10-3 is only good for 30 amps. Probably not enough to run a compressor and a welder at the same time.
 
OP
B

BaltimoreMatt

New member
Joined
Nov 23, 2010
Messages
3
Thanks. I probably won't be using both at the same time...I really just want the lights and one power tool, like the compressor or a table saw. I'll do some digging. Thanks again.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Better descriptions would help. Is the garage detached, or attached? Is the subpanel and the main panel both in the house? Both panels full?

Edit: Sorry, I just noticed the title tells us the garage is detached.

Charles
 
To avoid these ads, REGISTER NOW!

empty

Member
Joined
Dec 29, 2006
Messages
8
I have a similar situation and am looking for the same guidance.

Circuit already in detached garage with no subpanel, likely 20A because only runs some lights and a garage door opener with some outlets.
 
OP
B

BaltimoreMatt

New member
Joined
Nov 23, 2010
Messages
3
Charles, Thanks for the response, both the panels are full and located in the house. This was originally for an 8x14 shed, that had a couple lights and a single outlet. I'm not looking for enough juice to power the new garage as a full time workshop yet, I just was hoping to get those 8 4-bulb flourescents and a 6 outlets running with minimal interuption and hassle from the sub and the main. Think its possible?
Thanks
 