Electric to shed

tombarton

Member
Joined
May 26, 2024
Messages
5
Shed is 15 feet from house 200 amp panel. Want to add a box to shed to feed one light and one small 5K air conditioner. A 20 amp breaker already feeds one outdoor GFI plug nearby, attached to house. Got new 12/2 in conduit and want to pig tail it off that existing 20 amp GFI plug To source the shed. Can I do this safely as planned?
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,553
Location
Richmond, VA
What kind of wire is it? Hopefully not nm-b (romex) as it isn't allowed outdoors

Yes, with the right wire, you can extend the existing 20a circuit to your shed
 
OP
T

tombarton

Member
Joined
May 26, 2024
Messages
5
Thx. So what's the no no safety issue running rwo separate 12/2 underground rated wires to a shed. What's the reasoning behind it? If they are 6 ft apart and forever separate wires into a shed, why does code say it's a big no no?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,553
Location
Richmond, VA
with separate feeds, you need to take multiple steps to disconnect power to a structure. Also, it could create parallel pathways.

I believe that the latest code revision has changed this, but I'm not certain.

if you are considering running two circuits, just do a multi wire branch circuit. 12/3 uf-b or thwn-2 in conduit, fed by a two pole 20a breaker
 
Last edited:

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,169
Location
SE MI
if you are considering running two circuits, just do a multi wire branch circuit. 12/3 uf-b or thwn-2 in conduit, fed by a two pole 20a breaker
Don't quote me, but if it is a separate building, I think code requires a disconnect in the building.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,014
Location
Modesto, CA
Thx. So what's the no no safety issue running rwo separate 12/2 underground rated wires to a shed. What's the reasoning behind it? If they are 6 ft apart and forever separate wires into a shed, why does code say it's a big no no?
can you post a picture of the wire you have

NM-b is not rated for outdoor or underground use regardless of conduit.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,972
Location
Central Iowa
If your jurisdiction recognizes the 2020 or 2023 NEC, the single feed to a detached building is no longer an issue. You can have up to 6 feeds, but each needs a labeled, separate disconnecting means grouped together, in separate enclosures
The grouping is fine and makes perfect sense but I have issues with the separate enclosures. Ain't no way this fat guy is going to run six 20 amp circuits to a separate structure, but if I were to do so, I would think a six gang box would be better. The same goes for a 400 amp service and needing each of the 200 amp breakers behind it's own door (when installed outside as the emergency disconnect). Wouldn't it be easier for the fireman to open one door and kill both breakers even if one of them doesn't need to be shut off because it's for a shop? They could be labeled on the inside just as well if not better than the outside just to try to eliminate confusion.
 
OP
T

tombarton

Member
Joined
May 26, 2024
Messages
5
I already have 12/2 buried in conduit to the shed so to late to change wire. My first mistake. If I add a cut off breaker on the shed and keep the air conditioner to small at 5 k btu plus one shed light, I should be ok. Yes? Reaction appreciated. Just curious as to whats the reading behind code? Parallel pathways.? What the hell is that about? . Where’s the danger there. Two runs 6 ft apart buried parallel 15 ft long to a small shed. What’s the danger look like? I can live with it just a homeowner ya know what’s the reasoning here. In my house I have parallel lines all over the place. Difference must be related to it being outdoors in the ground to a shed 15 ft away from the house. I guess. What goes wrong worse case scenario
What kind of wire is it? Hopefully not nm-b (romex) as it isn't allowed outdoors

Yes, with the right wire, you can extend the existing 20a circuit to your shed
wire is rated underground 12 2 ya know the hard stuff that takes a day to strip
 
OP
T

tombarton

Member
Joined
May 26, 2024
Messages
5
The grouping is fine and makes perfect sense but I have issues with the separate enclosures. Ain't no way this fat guy is going to run six 20 amp circuits to a separate structure, but if I were to do so, I would think a six gang box would be better. The same goes for a 400 amp service and needing each of the 200 amp breakers behind it's own door (when installed outside as the emergency disconnect). Wouldn't it be easier for the fireman to open one door and kill both breakers even if one of them doesn't need to be shut off because it's for a shop? They could be labeled on the inside just as well if not better than the outside just to try to eliminate confusion.
So 2 shut off boxes in two locations for the firemen. I can do that. And little danger with two 12/2 buried lines to a shed? do they have to be buried separately I wonder?
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,972
Location
Central Iowa
So 2 shut off boxes in two locations for the firemen. I can do that. And little danger with two 12/2 buried lines to a shed? do they have to be buried separately I wonder?
AFAIK they can be in same trench, but I've never had to find out. If you're going back to the panel to get circuit #2 why not just bring a 12/3 and have two circuits exclusively for the shed? Then there's nothing to worry about and you can use one two pole switch for a disconnect
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,893
The grouping is fine and makes perfect sense but I have issues with the separate enclosures. Ain't no way this fat guy is going to run six 20 amp circuits to a separate structure, but if I were to do so, I would think a six gang box would be better. The same goes for a 400 amp service and needing each of the 200 amp breakers behind it's own door (when installed outside as the emergency disconnect). Wouldn't it be easier for the fireman to open one door and kill both breakers even if one of them doesn't need to be shut off because it's for a shop? They could be labeled on the inside just as well if not better than the outside just to try to eliminate confusion.

Reduces the maximum available fault current, which reduces the maximum energy an arc flash can have.
 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,972
Location
Central Iowa
Reduces the maximum available fault current, which reduces the maximum energy an arc flash can have.
The 400 amp meter setting with two 200 amp breakers is the same as the pre 2020 service with the difference being that instead of both breakers being behind a 12" wide door, they are now behind separate 6" wide doors. Fault current isn't changed by adding another step to shut everything off and it's only a consideration in commercial services.
 
OP
T

tombarton

Member
Joined
May 26, 2024
Messages
5
Thx. So what's the no no safety issue running rwo separate 12/2 underground rated wires to a shed. What's the reasoning behind it? If they are 6 ft apart and forever separate wires into a shed, why does code say it's a big no no?
Apparently the reasoning 2 separate circuits are not allowed is an unknowing resident might think they have turned off the power to the shed by flipping the panel breaker when in fact one plug in the shed is still hot! Dangerous! Got my answer thx. I'll follow code.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,972
Location
Central Iowa
Apparently the reasoning 2 separate circuits are not allowed is an unknowing resident might think they have turned off the power to the shed by flipping the panel breaker when in fact one plug in the shed is still hot! Dangerous! Got my answer thx. I'll follow code.
That probably was the reason, but as of the adoption of the 2020 NEC, more than one circuit can be run to another building. The safety factor is why disconnects are supposed to be grouped together.
 

thool

Well-known member
Joined
Jun 23, 2015
Messages
5,307
Location
Rochester, NY
To avoid creating another thread with similar content, I'm going to piggyback on this one.

If someone has a shed that is about 3 feet from a 100A mobile home, and they want to provide 15A power to a single outlet and a couple switched hardwired LED lights in the shed, how would this imaginary person go about this safely? Would a GFCI breaker, followed by direct burial UF-B be appropriate?

Thinking 2 boxes: the first in line would be a 2-gang with a switched outlet, the second/downstream would be a single for the light switch.

The most the outlet will be for would be charging batteries for lawnmower, cordless tools, sometimes a boat battery, wired drill. Possibly a small 2 gallon air compressor.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,972
Location
Central Iowa
To avoid creating another thread with similar content, I'm going to piggyback on this one.

If someone has a shed that is about 3 feet from a 100A mobile home, and they want to provide 15A power to a single outlet and a couple switched hardwired LED lights in the shed, how would this imaginary person go about this safely? Would a GFCI breaker, followed by direct burial UF-B be appropriate?
A GFCI breaker is fine, but I would use a regular breaker and GFCI receptacles
Thinking 2 boxes: the first in line would be a 2-gang with a switched outlet, the second/downstream would be a single for the light switch.

The most the outlet will be for would be charging batteries for lawnmower, cordless tools, sometimes a boat battery, wired drill. Possibly a small 2 gallon air compressor.
You need a disconnect on or in the shed that will shut everything off. The first box, whether on the outside or inside should have a switch that kills everything in there and from there you can split lights and receptacles.
 

thool

Well-known member
Joined
Jun 23, 2015
Messages
5,307
Location
Rochester, NY
A GFCI breaker is fine, but I would use a regular breaker and GFCI receptacles
If I used a plain breaker, then wouldn't everything between it and the GFCI receptacle be unsafe?

You need a disconnect on or in the shed that will shut everything off. The first box, whether on the outside or inside should have a switch that kills everything in there and from there you can split lights and receptacles.
Is there a special part for the disconnect, or would an ordinary switch be sufficient?
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,972
Location
Central Iowa
If I used a plain breaker, then wouldn't everything between it and the GFCI receptacle be unsafe?
What is there to be unsafe? It's either going to be three wires in conduit or three wires in a cable assembly (UF) with no devices, the only real concern would be if the conductors were cut and the grounding conductor should take care of that. If you want to use a GFCI breaker, then by all means, go for it. The lights in the shed don't have to have GFCI protection unless they plug in and a GFCI breaker is a good way to be standing in the dark some evening.
Is there a special part for the disconnect, or would an ordinary switch be sufficient?
A plain old single pole switch will work just fine.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,014
Location
Modesto, CA
If I used a plain breaker, then wouldn't everything between it and the GFCI receptacle be unsafe?
unless the wires underground get cut, there shouldnt be an issue.

the problem with using a GFCI breaker in this scenario is if it trips and youre in the shed, youll be left in the dark. better to have a receptacle GFCI to keep the lights on
 

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,325
Location
Alexandria, VA
You also have the option to use 12/3 or 14/3 UF-B and at the shed you can break it out into two circuits and use a GFCI on each circuit. However, it sounds like two circuits are more than you need for your requirements.
 

thool

Well-known member
Joined
Jun 23, 2015
Messages
5,307
Location
Rochester, NY
You also have the option to use 12/3 or 14/3 UF-B and at the shed you can break it out into two circuits and use a GFCI on each circuit. However, it sounds like two circuits are more than you need for your requirements.
Thanks, but all I need is the 1 circuit.
 

ipgenie

Well-known member
Joined
Jan 29, 2020
Messages
561
Location
Idaho
Another option I've seen that I 'think' is kosher is to put a GFCI receptical on the house at the panel, then use an extension cord to connect the shed wiring to that receptical. Basically what an RV uses. The cord could be hard wired on the shed side or connected to a generator inlet. Unplugging the cord from the house provides the means of disconnect and the full path is GFCI protected.

If course this means you would be OK with a 3 foot cord between buildings which probably doesn't work if it crosses a sidewalk.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,553
Location
Richmond, VA
Another option I've seen that I 'think' is kosher is to put a GFCI receptical on the house at the panel, then use an extension cord to connect the shed wiring to that receptical. Basically what an RV uses. The cord could be hard wired on the shed side or connected to a generator inlet. Unplugging the cord from the house provides the means of disconnect and the full path is GFCI protected.

If course this means you would be OK with a 3 foot cord between buildings which probably doesn't work if it crosses a sidewalk.
Cords are for temporary use only. It will function but really isn't the right way to do it
 